Author Topic: [Reward FOR answers] 50TH S1 Farm  (Read 3065 times)
Trends
Member
**
Offline Offline

Activity: 119
Merit: 10


View Profile
May 09, 2014, 01:39:36 AM
 #21

Maybe Industrial with 440V or 575V

Quadriga CX BTC/CAD Coin Exchange     www.quadrigacx.com/?ref=umvq5t3i2r6im243v94vucbo
philipma1957
Legendary
*
Offline Offline

Activity: 4312
Merit: 8873


'The right to privacy matters'


View Profile WWW
May 09, 2014, 01:40:51 AM
 #22

kendog is correct that 400 amps does not  do  100k watts unless the power is 440 multi phase   but at 220 208 or 110 not enough power.

oh my last shot of  the six ants running

you want ant monitor  the monitor I am using  link

https://bitcointalk.org/index.php?topic=596178.msg6548589#msg6548589

but start small  maybe 15  or get 3 of the 16 port switches.

  do 1 into 2.  check for latency issues   since 1 switch can do 15 switches giving you 200 plus ants.

feel free to ask me in a pm about setting up but frankly I am not a fan of the dells




▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Taugeran
Hero Member
*****
Offline Offline

Activity: 658
Merit: 500


CCNA: There i fixed the internet.


View Profile
May 09, 2014, 02:31:54 AM
 #23

There's a new 1500 watt psu from corsair that 80 PLUS TITANIUM CERTIFIED

94% peak efficiency, 125 amps at 12 volts, single rail


Corsair ax1500i. It's an absolute monster

Bitfury HW & Habañero : 1.625Th/s
tips/Donations: 1NoS89H3Mr6U5CmP4VwWzU2318JEMxHL1
Come join Coinbase
BTCBuyer (OP)
Full Member
***
Offline Offline

Activity: 177
Merit: 100



View Profile WWW
May 09, 2014, 02:55:55 AM
 #24

Yoshi at Bitmain is recommending Either Dell 750W Server PSU or the HP 1200W Server PSU, for the most economic solution. Your thoughts?
thomas_s
Hero Member
*****
Offline Offline

Activity: 574
Merit: 500


View Profile
May 09, 2014, 03:02:23 AM
 #25

Yoshi at Bitmain is recommending Either Dell 750W Server PSU or the HP 1200W Server PSU, for the most economic solution. Your thoughts?
We used the Dell 750's on all the S1's for our hosting customers
klondike_bar
Legendary
*
Offline Offline

Activity: 2128
Merit: 1005

ASIC Wannabe


View Profile
May 09, 2014, 03:21:32 AM
 #26

theres a really weird mix of advice in this thread, a lot of it coming from people with less than 5 antminers.

I currently run 17 antminers (and have run/sold several more on top of that). Here is my advice.

1) go with 208V power. If you are industrial you likely have 600V mains, and 208V is the most common transformer output. Its also about 3-5% more efficient than 120V.
2) use L6-30 outlets and find some PDUs (power distribution units) that match it. This gives ~4.98kW of power per outlet (after the 20% safety threshold) and is a common style that is cheap to find and install
3) get a few 48-port network switches that are 10/100 outputs. Most of these are build with a gigabit trunk so they can all daisy chain while providing plenty of good connections.
4) forget the secondary fans. Its an extra cost, wastes time to install, and is totally unnecessary in the setup you are going for.

5) you NEED the ability to ventilate the heat directly outside. a closed building requires much more air conditioning and thus even more power usage.
5b) use a hot/cold aisle design. 2 rows of shelves, exhaust from both pinted inwards, with strong fans pushing all the heat out the aforementioned ventilation to outside.
5c) you will still need a lot of AC to keep things cool, probably about 15% of the ASIC power draw if you can vent to outdoors, 30% otherwise.

6) go with DPS-2000 power supplies. These are the most effective use of space and time for getting the massive 12V amperage you will need. Alternatively, the DPS-800 can put out 1000W on a 208V input. (gigampz.com has some nice, but slightly pricy, breakout boards to make using this PSU easy)
6b) soldering fat wires to a PSU is a huge pain. either follow a method that requires minimal soldering, or invest in a proper 120W+ soldering gun that is at least $40. anything cheaper will burn up with extended use.
6c) I sell custom 16awg PCIe cables with tinned ends. They are thick wires and can handle more than enough current (beware 18awg labelled stuff from china). see my sig if you are interested in getting some - they work well if you splice a few onto thicker 10 or 12 awg wires for use with the DPS-2000.
6ci) PCIe connectors will make life easy if something needs swapping. the screw terminals are impossible to access if you stack miners or have them side by side.

7) stack the miners on thier sides,with bottoms facing the bottoms of those in the neighbouring stack. (see picture).  This will allow you to pack miners in with good density and contain the airflow across the units nicely.





Yes, the SP10 is smaller and more efficient. But it costs almost twice the $/GH. If you are bullish on BTC prices rising the S1 is by far the best option. (if you feel that in 6 months from now we will still be <$500, then by all means go for the more efficient hardware). The S1 is a solid unit with nice 120mm fans, and if you have the space and power for them they are my #1 pick.    You can always undervolt them (takes about 5-10 min per machine to do) to get <1.3w/GH when the time comes  (about 2 months by my estimate if $/BTC doesn't jump up first)

24" PCI-E cables with 16AWG wires and stripped ends - great for server PSU mods, best prices https://bitcointalk.org/index.php?topic=563461
No longer a wannabe - now an ASIC owner!
thomas_s
Hero Member
*****
Offline Offline

Activity: 574
Merit: 500


View Profile
May 09, 2014, 03:30:19 AM
 #27

theres a really weird mix of advice in this thread, a lot of it coming from people with less than 5 antminers.

I currently run 17 antminers (and have run/sold several more on top of that). Here is my advice.

1) go with 208V power. If you are industrial you likely have 600V mains, and 208V is the most common transformer output. Its also about 3-5% more efficient than 120V.
2) use L6-30 outlets and find some PDUs (power distribution units) that match it. This gives ~4.98kW of power per outlet (after the 20% safety threshold) and is a common style that is cheap to find and install
3) get a few 48-port network switches that are 10/100 outputs. Most of these are build with a gigabit trunk so they can all daisy chain while providing plenty of good connections.
4) forget the secondary fans. Its an extra cost, wastes time to install, and is totally unnecessary in the setup you are going for.

5) you NEED the ability to ventilate the heat directly outside. a closed building requires much more air conditioning and thus even more power usage.
5b) use a hot/cold aisle design. 2 rows of shelves, exhaust from both pinted inwards, with strong fans pushing all the heat out the aforementioned ventilation to outside.
5c) you will still need a lot of AC to keep things cool, probably about 15% of the ASIC power draw if you can vent to outdoors, 30% otherwise.

6) go with DPS-2000 power supplies. These are the most effective use of space and time for getting the massive 12V amperage you will need. Alternatively, the DPS-800 can put out 1000W on a 208V input. (gigampz.com has some nice, but slightly pricy, breakout boards to make using this PSU easy)
6b) soldering fat wires to a PSU is a huge pain. either follow a method that requires minimal soldering, or invest in a proper 120W+ soldering gun that is at least $40. anything cheaper will burn up with extended use.
6c) I sell custom 16awg PCIe cables with tinned ends. They are thick wires and can handle more than enough current (beware 18awg labelled stuff from china). see my sig if you are interested in getting some - they work well if you splice a few onto thicker 10 or 12 awg wires for use with the DPS-2000.
6ci) PCIe connectors will make life easy if something needs swapping. the screw terminals are impossible to access if you stack miners or have them side by side.

7) stack the miners on thier sides,with bottoms facing the bottoms of those in the neighbouring stack. (see picture).  This will allow you to pack miners in with good density and contain the airflow across the units nicely.





Yes, the SP10 is smaller and more efficient. But it costs almost twice the $/GH. If you are bullish on BTC prices rising the S1 is by far the best option. (if you feel that in 6 months from now we will still be <$500, then by all means go for the more efficient hardware). The S1 is a solid unit with nice 120mm fans, and if you have the space and power for them they are my #1 pick.    You can always undervolt them (takes about 5-10 min per machine to do) to get <1.3w/GH when the time comes  (about 2 months by my estimate if $/BTC doesn't jump up first)

+1
Powell
Sr. Member
****
Offline Offline

Activity: 486
Merit: 262

rm -rf stupidity


View Profile
May 09, 2014, 03:48:32 AM
 #28

How do you plan on cooling the usable 400A of power.  Have to have power reserved for that.

I skimmed most of the post and only thing mentioned is fans.  Which with the amount of Antminers or hell any miner you have to have proper cooling for it.

Watts to BTU/hr = 3.412141633 x Watts
RT (Refrigerated Tons) from BTU/hr = BTU/hr / 12000

Or at that scale you would be buying an AC setup for a datacenter style where you would be looking at it as kW being used like with a Liebert, etc. unit.
Kaega
Full Member
***
Offline Offline

Activity: 158
Merit: 100


View Profile
May 09, 2014, 05:15:49 AM
 #29

oh you need two internet lines not one if you go over 250 or 256.

a router taps out at  amax of 256 including the router     192.168.0.   1- 256     these 1-256 are the most you can do on 1 router.


Learn how to internets.

Use the 10.x.x.x and setup a Class A or B network. 


Protect your coin: Buy a Treznor
Angela8488
Full Member
***
Offline Offline

Activity: 127
Merit: 100


View Profile
May 09, 2014, 05:26:20 AM
 #30

If it were me, I would certainly not hesitate to use a wireless connection, even if it will be difficult to manage
dogie
Legendary
*
Offline Offline

Activity: 1666
Merit: 1185


dogiecoin.com


View Profile WWW
May 09, 2014, 06:07:33 AM
 #31

See my Sig for setup guide. 200 is the same as 1.

ElGabo
Hero Member
*****
Offline Offline

Activity: 635
Merit: 500


View Profile
May 09, 2014, 07:16:57 AM
 #32

If it were me, I would certainly not hesitate to use a wireless connection, even if it will be difficult to manage

Never mine with wi-fi....

But to stay on topic

Just a small batch:



And a part of...



But trust me, better go for larger machines in smaller quantities...  Wink


" I'm waiting for my punishment, I know it's on my way
  So cut, cut, cut me up and fuck, fuck, fuck me up"
philipma1957
Legendary
*
Offline Offline

Activity: 4312
Merit: 8873


'The right to privacy matters'


View Profile WWW
May 09, 2014, 11:49:06 AM
 #33





But trust me, better go for larger machines in smaller quantities...  Wink



The long solid shelf you use make for a nice wind tunnel effect along with side by side for 10 or 12 miners.   those look like mdf so they won't allow heat to rise much


that setup could be improved using simple 20 inch box fans on the pull side venting much of the heat out of the building.

   obviously I am trying to get the op to avoid/lower ac cost as much as possible.

you have close to 40 in that setup the op would need 5 to 7  racks like that.  his biggest problem with your setup is access to the gear. but with 200 plus s-'1 anything other then a line of lunch tables makes the same problem.

 btw  if he gets some 1th machines it is less work.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
ElGabo
Hero Member
*****
Offline Offline

Activity: 635
Merit: 500


View Profile
May 09, 2014, 02:53:22 PM
 #34





But trust me, better go for larger machines in smaller quantities...  Wink



The long solid shelf you use make for a nice wind tunnel effect along with side by side for 10 or 12 miners.   those look like mdf so they won't allow heat to rise much


that setup could be improved using simple 20 inch box fans on the pull side venting much of the heat out of the building.

   obviously I am trying to get the op to avoid/lower ac cost as much as possible.

you have close to 40 in that setup the op would need 5 to 7  racks like that.  his biggest problem with your setup is access to the gear. but with 200 plus s-'1 anything other then a line of lunch tables makes the same problem.

 btw  if he gets some 1th machines it is less work.

I have an 22000 air m3/h industrial fan in the wall at the back of the shelf to suck out the warm air. Smiley

I've made the height of the shelf small because I didn't had more space. The new shelf is higher, have more space at the top of the miners, but no space between them because the cooling is better this way.

I have an other shelf but it's not shown at the picture.

I'll try to make a paint but don't laugh hard.  Grin



Had had to do this way because of the spec of the room.

If I'll able to make a new room, and If i were op i'd do this. (I'll sure do it when I arrive that point to make a new room.)



You still have enough room to check the miners.

But I'll definitely go for 1 th or bigger machines.


" I'm waiting for my punishment, I know it's on my way
  So cut, cut, cut me up and fuck, fuck, fuck me up"
elcuim
Newbie
*
Offline Offline

Activity: 2
Merit: 0


View Profile
May 09, 2014, 04:53:10 PM
 #35

Hi Everyone,


I am setting up a 50TH S1 Farm

Those of you with experience on setting up larger S1 FARMS, are there anything I should be aware of?

I read that you can use server power supplies as they are cheaper, but it looks like there's quite a bit of work behind setting up the PSU for 278 machines.

What would be the most cost efficient PSU setup? What type of networking Issues should I be aware of? What is the most efficient set up? How would you deal with airflow and heat?

What is the best type of RACK to set up on?

I look forward to all your experiences, creative solutions, and help.


BTCBuyer

First you be careful with heat from ants. You can make a tower with the ants and create a wind tunnel effect to easily exhaust the heat from building you can put a big fan.

In the electric problem each ant eat 360w from the wall so if you put 278 miners you need a 100Kw line in 220v.. You needs many main switches for isolate electric problems. Dell server power supply make extreme noise. Really EXTREME. Consider hp 1000W server power supply have less noise and it's more easily for hack and make the wire connections...

For 278 ants you possibly have to pay a bill near to 5000USD / month.. nice

Additional you need control the humidity of the air and playing with this you can increase the refrigeration of the facility.

For the network you need a gigabit main router you need a gigabit enterprise router o business router. And many 48th lines 100mb switches with less than 1 gigabit line to connect with the main router. And can use a watchdog for reset automatically every ant when this stop mining for any reason.

Happy mining!
philipma1957
Legendary
*
Offline Offline

Activity: 4312
Merit: 8873


'The right to privacy matters'


View Profile WWW
May 09, 2014, 05:02:18 PM
 #36

now if the op wants he could get

1th miners from bitmaintech   the price is now 2529 - 400 usd if you have a coupon

  at 2129  they are pretty tempting .  he can pull 1 board from each one  as it gives the stock psu overhead. 

 sell a few boards on ebay keep a few board for spares.

 much easier to manage. 45-50 machines then 250plus .

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
Syke
Legendary
*
Offline Offline

Activity: 3878
Merit: 1193


View Profile
May 09, 2014, 06:08:55 PM
 #37

If you're going to do 50TH, forget the S1. Get 36 SP10s instead. Call up Spondoolies and I'm sure you get can a discount for a 36 unit order. Setting up 36 units would be a piece of cake.

Buy & Hold
philipma1957
Legendary
*
Offline Offline

Activity: 4312
Merit: 8873


'The right to privacy matters'


View Profile WWW
May 09, 2014, 07:25:23 PM
 #38

If you're going to do 50TH, forget the S1. Get 36 SP10s instead. Call up Spondoolies and I'm sure you get can a discount for a 36 unit order. Setting up 36 units would be a piece of cake.

if he could get  30 sp10s at the right price it is the best way to go.

 not sure if they go low for a 30 unit buy.

▄▄███████▄▄
▄██████████████▄
▄██████████████████▄
▄████▀▀▀▀███▀▀▀▀█████▄
▄█████████████▄█▀████▄
███████████▄███████████
██████████▄█▀███████████
██████████▀████████████
▀█████▄█▀█████████████▀
▀████▄▄▄▄███▄▄▄▄████▀
▀██████████████████▀
▀███████████████▀
▀▀███████▀▀
.
 MΞTAWIN  THE FIRST WEB3 CASINO   
.
.. PLAY NOW ..
tzortz
Hero Member
*****
Offline Offline

Activity: 728
Merit: 500



View Profile
May 09, 2014, 11:10:20 PM
 #39

I think they say they give different price for orders >50 pcs.
 I am not quite sure, but give them a call.

All is Mine!

1H7LUdfx9AFTMSXPsCBror3RDk57zgnc2R
solarion
Hero Member
*****
Offline Offline

Activity: 966
Merit: 513



View Profile
May 09, 2014, 11:40:19 PM
 #40

Good suggestions in this thread.

I'm running 30 s1's each with an individual psu. After much consideration I chose the the rosewill capstone 550w 80+ gold psu from amazon($74 each w/ shipping). An overclocked s1 on 220v lands squarely in it's peak efficiency range. For secondary fans I'm running delta afb1212she(150cfm). The ants are arrayed horizontally on heavy duty plastic grate type shelving units with each corresponding psu located on the shelf beneath.

For ventilating the room the ants are in I utilize (6)14" industrial fans arrayed in pairs on the room's three windows. Two pairs of fans pull fresh air in and the pair nearest the ants exhausts the heat. In addition there are (3)20" industrial fans pushing air around in this long room.

CGRemote is used to control the chaos.

While it's loud and ambient is peaking around 90f during the day near the ants I haven't had a single failure(psu or ant) in the three months I've been running this way.