With a standard 100 amp residential supply my consumer unit is split up with a number of RCD's.

My garage which hosts all my mining equipment has an RCD of B40 (I assume that's 40 amps), on the main board, with an RCD in the garage too.

Does this mean the totality of my miner consumption must not exceed 40amps, calculated as PSU Watts/240V.

For example if I have an Antminer S4, which has a 1.4kW PSU, this is consuming 5.8amps? Therefore I can only have 40/5.8 = 6 S4's on this RCD?

Or is the consumption and the RCD related in a different way.

The reason I ask is that if was to bulk buy the 16 S4's from Bitmain (ignore ROI for now Smiley), I would need effectively 4 B40 RCD's?


Have I understood that correctly?
Thanks
Rob
dogjunior
Sr. Member
****
Offline Offline

Activity: 407
Merit: 255


View Profile
December 15, 2014, 10:43:53 PM
 #2

What country are in? Most newer homes in the United States have a 200 amp residential panel. The circuit breakers in the panel are generally rated 15 to 20 amps and are shared by one or two outlets.  16 S4 at 1400 watts per S4 you are looking at 22,400 watts.  No way you can run this many S4's with only 100 amps.
Blobby (OP)
Newbie
*
Offline Offline

Activity: 10
Merit: 0


View Profile
December 15, 2014, 10:51:27 PM
 #3

I'm in the UK
Homes here have a standard 100 amp supply, with 240V wall sockets.

I'm not expecting to be able to run them all, but just wanting to confirm my understanding in terms of what the RCD rating allows. As the total of all the RCDs in the panel exceed 100amps.
xstr8guy
Hero Member
*****
Offline Offline

Activity: 784
Merit: 1004


Glow Stick Dance!


View Profile
December 15, 2014, 11:01:08 PM
 #4

What's an RCD?
PuertoLibre
Legendary
*
Offline Offline

Activity: 1848
Merit: 1003


View Profile
December 15, 2014, 11:04:18 PM
 #5

What's an RCD?
http://en.wikipedia.org/wiki/Residual-current_device
Blobby (OP)
Newbie
*
Offline Offline

Activity: 10
Merit: 0


View Profile
December 15, 2014, 11:07:18 PM
 #6

if it helps, picture of board here:
https://i.imgur.com/0fvNwY7.jpg
dogjunior
Sr. Member
****
Offline Offline

Activity: 407
Merit: 255


View Profile
December 15, 2014, 11:15:55 PM
 #7

1.4 kW will pull about 5.8 amps at  240v so you are safe to put 5 maybe 6 on your circuit. How many outlets are you sharing on the circuit? To add more you would need to upgrade the panel to 200A then you could add 2 more 40A RCD's. Also I would spread the amps over multiple outlets because the wiring in one outlet is probably not sufficient to handle 40A.
Syke
Legendary
*
Offline Offline

Activity: 3878
Merit: 1193


View Profile
December 15, 2014, 11:20:17 PM
 #8

For example if I have an Antminer S4, which has a 1.4kW PSU, this is consuming 5.8amps? Therefore I can only have 40/5.8 = 6 S4's on this RCD?

Almost. You shouldn't run a circuit above 80% continuous. So keep your 40 amp circuit at 32 amps or less. 32/5.8 = 5x S4s.

Buy & Hold
Blobby (OP)
Newbie
*
Offline Offline

Activity: 10
Merit: 0


View Profile
December 15, 2014, 11:23:27 PM
 #9

For example if I have an Antminer S4, which has a 1.4kW PSU, this is consuming 5.8amps? Therefore I can only have 40/5.8 = 6 S4's on this RCD?

Almost. You shouldn't run a circuit above 80% continuous. So keep your 40 amp circuit at 32 amps or less. 32/5.8 = 5x S4s.

That may explain why I have a 32 amp breaker in the garage on that circuit.

Thanks for your help. It confirmed my thoughts and then some.

Regards
Rob
Zich
Legendary
*
Offline Offline

Activity: 1190
Merit: 1000


View Profile WWW
December 16, 2014, 01:57:50 AM
Last edit: December 16, 2014, 02:19:14 AM by Zich
 #10

Your garage supply not using RCD, it's MCB  Smiley
It's seem connected directly to main switch, not through 80A RCD. Can't be sure unless you can open the cover & take more detail picture  Grin

But still, the maximum you can pull is 100A minus other load on RCD.
Example, if load on RCD already 70 A, then maximum load is 30A


wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
December 16, 2014, 03:55:44 AM
 #11

1.4 kW will pull about 5.8 amps at  240v so you are safe to put 5 maybe 6 on your circuit. How many outlets are you sharing on the circuit? To add more you would need to upgrade the panel to 200A then you could add 2 more 40A RCD's. Also I would spread the amps over multiple outlets because the wiring in one outlet is probably not sufficient to handle 40A.

For example if I have an Antminer S4, which has a 1.4kW PSU, this is consuming 5.8amps? Therefore I can only have 40/5.8 = 6 S4's on this RCD?

Almost. You shouldn't run a circuit above 80% continuous. So keep your 40 amp circuit at 32 amps or less. 32/5.8 = 5x S4s.

You should NOT give electrical advice assuming that the UK electrical circuits are similar with your US ones. Please, for heaven's sake .. grow up .. or the OP will need a new home soon. The only similar thing is that they have plugs .. see an example below:


CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
Syke
Legendary
*
Offline Offline

Activity: 3878
Merit: 1193


View Profile
December 16, 2014, 04:52:41 AM
 #12

You should NOT give electrical advice assuming that the UK electrical circuits are similar with your US ones. Please, for heaven's sake .. grow up .. or the OP will need a new home soon. The only similar thing is that they have plugs .. see an example below:

http://upload.wikimedia.org/wikipedia/commons/thumb/8/81/Consumer_Mains_Wiring.jpg/640px-Consumer_Mains_Wiring.jpg

Interesting. Tell us more. Do you suggest running a UK 40 amp circuit at higher than 80% continuous load 24/7?

Buy & Hold
discoverag
Newbie
*
Offline Offline

Activity: 7
Merit: 0


View Profile
December 16, 2014, 03:27:04 PM
 #13

I am running Antminer S4. If the voltage from the mains is a perfect 230V, then it will take 6.2 A at the wall.
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
December 16, 2014, 03:57:12 PM
 #14

You should NOT give electrical advice assuming that the UK electrical circuits are similar with your US ones. Please, for heaven's sake .. grow up .. or the OP will need a new home soon. The only similar thing is that they have plugs .. see an example below:

http://upload.wikimedia.org/wikipedia/commons/thumb/8/81/Consumer_Mains_Wiring.jpg/640px-Consumer_Mains_Wiring.jpg

Interesting. Tell us more. Do you suggest running a UK 40 amp circuit at higher than 80% continuous load 24/7?

No. I suggest trying to refrain giving advice when you have no clue  (or only assumed clues) of the actual circuit setup in a country with different electrical codes than yours.
There's only ONE RCD in the picture. The things labelled B40, B32 B20 etc are NOT RCDs. There's a reason why this profession is regulated.

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
FeedbackLoop
Hero Member
*****
Offline Offline

Activity: 742
Merit: 500



View Profile
December 16, 2014, 05:12:46 PM
 #15


You should NOT give electrical advice assuming that the UK electrical circuits are similar with your US ones. Please, for heaven's sake .. grow up .. or the OP will need a new home soon. The only similar thing is that they have plugs .. see an example below:


That diagram seems to show both a neutral and a ground. Both exist in the UK? Don't they use a delta configuration for most of EU to save copper? Are both supplied by the sub-station?

[braces for rant]

Syke
Legendary
*
Offline Offline

Activity: 3878
Merit: 1193


View Profile
December 16, 2014, 05:33:24 PM
 #16

No. I suggest trying to refrain giving advice when you have no clue  (or only assumed clues) of the actual circuit setup in a country with different electrical codes than yours.
There's only ONE RCD in the picture. The things labelled B40, B32 B20 etc are NOT RCDs. There's a reason why this profession is regulated.

So what does your electrical code specify for the maximum continuous load on a 40 amp circuit?

Buy & Hold
wh00per
Hero Member
*****
Offline Offline

Activity: 571
Merit: 500



View Profile
December 16, 2014, 07:17:24 PM
 #17

No. I suggest trying to refrain giving advice when you have no clue  (or only assumed clues) of the actual circuit setup in a country with different electrical codes than yours.
There's only ONE RCD in the picture. The things labelled B40, B32 B20 etc are NOT RCDs. There's a reason why this profession is regulated.

So what does your electrical code specify for the maximum continuous load on a 40 amp circuit?

It's not about what the Canadian code specifies and when. How do you know it is a 40 amp circuit? He has a 100A main breaker and if you add every number you see in the picture you get way more than that (162, right?). Did you ask what other loads he has in the house?  The RCD is good up to 80A for his whole house (except the garage), which leaves only 20A for the garage. I hope she still wants to live there ..  the rest of the house still needs enough juice for the oven, boiler .. etc. He'll trip his pants out, or do some "arc-welding" in that panel if everything start at once, as after a temporary blackout or mains disconnect.

Maxing out a 40amp circuit (as per your understanding, with 32A continuous) when that circuit is not there might burn his garage out. The issue here is that you started giving advice based on what you think he has on in there .. and if he follows your advice he might burn his house down. I wonder how you can sleep at night ..

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
Test User
Member
**
Offline Offline

Activity: 85
Merit: 10

Miner and technician


View Profile
December 16, 2014, 07:25:02 PM
Last edit: December 16, 2014, 07:43:53 PM by Test User
 #18

That diagram seems to show both a neutral and a ground. Both exist in the UK? Don't they use a delta configuration for most of EU to save copper? Are both supplied by the sub-station?

Yes. Neutral and ground are separate.
No. Delta is not used at low voltage. The final service voltage is 230/400V wye.  In Uk, most residential is single phase 100A @ 230V. Large residences and small commercial premises will usually have 3 phase 100A @ 230/400V.

Whether both neutral and ground are supplied by the sub-station depends on the type of service and cabling.
TN-S (separate earth supplied by substation), TN-C-S (combined neutral/earth supplied by substation, with redundant earthing in transit and separated at point of service drop) and TT (no earth connection provided by substation, customer provides earth rod at service entrance) are all common.

Quote
So what does your electrical code specify for the maximum continuous load on a 40 amp circuit?

Maximum continuous load on a 40A circuit is 40 A. No derating is required for load duration (doesn't stop it being a good idea), and in general is not performed. For example, no specific derating is needed for a 3.1 kW storage heater which is designed to take full load for 7 hours to charge it's thermal store, and the closest circuit capacity available (16 A) can be used. Typical installation cable is 1.5 mm2 flex (for final connection) and 2.5 mm2 in-wall wiring (derated due to thermal insulation).

Derating is performed based upon ambient temperature, cable grouping, cable mounting surface and insulation.

Donations welcome - BTC: 1f52PwRLHkN4w5uBY6EccKiDYqpLkh13y     DOGE: DCg65AKPG76X5LEtWCqfyRj4a6apYRHR8j
Trust: https://bitcointalk.org/index.php?topic=432215.0
IITravel01
Sr. Member
****
Offline Offline

Activity: 338
Merit: 250


View Profile
December 16, 2014, 07:52:17 PM
 #19

To me it looks like he's got 100A for the whole house, 40A breaker for the garage and 80A for the rest of the house.  Wouldn't that allow up to 40A (at 230v = 9,200Watts) in the garage (if at full load, that would leave 60A for the rest of the house) or 80A for the rest of the house (leaving 20A for the garage).  If it goes over 100A for both then shouldn't the main 100A breaker flip?  So he should be able to use up to 40A in the garage, as long as his rest of the house load isn't over 60A?  If it goes over, shouldn't the main 100A breaker flip and then no the house wouldn't theoretically burn down?  (wh00per, that's a question mark there just in case you're not sure I'm asking a question).
Test User
Member
**
Offline Offline

Activity: 85
Merit: 10

Miner and technician


View Profile
December 16, 2014, 07:57:38 PM
Last edit: December 16, 2014, 08:11:08 PM by Test User
 #20

To me it looks like he's got 100A for the whole house, 40A breaker for the garage and 80A for the rest of the house.  Wouldn't that allow up to 40A (9,200Watts) in the garage (if at full load, that would leave 60A for the rest of the house) or 80A for the rest of the house (leaving 20A for the garage).  If it goes over 100A for both then shouldn't the main 100A breaker flip?  So he should be able to use up to 40A in the garage, as long as his rest of the house load isn't over 60A?  If it goes over, shouldn't the main 100A breaker flip and then no the house wouldn't theoretically burn down?  (whooper, that's a question mark there just in case you're not sure I'm asking a question).

Yes. That's basically correct. He's limited by the 100 A service (fuse, not circuit breaker).
His "in house" consumption is limited by the 80A rating of the RCD. However, if he is drawing substantial power in the garage, then it will be limited by the total load on the 100A main switch and fuse.

So, if he exceeds 100A, he will blow out the sealed service fuse, and then have to call the power company to come out, unseal it and replace the fuse and reseal.

The big problem he has in his house is the electric shower. As this has a 50 A dedicated circuit, this suggests that it is a 10.8 kW shower (45A operating load). That is a big load, and once you add lighting loads, kitchen loads, etc. a 40A mining load is starting to look infeasible.

One option is to upgrade the supply from a 230V (23 kW) supply to a 230/400V (70 kW) supply. If he asks his electricity supplier they will quote on the price of an upgrade (usually it's around £2000-£3000), and it'll be another £500-800 for an electrician to replace the fusebox with a 400 V one + another £few hundred for additional circuit installation. In reality, this probably isn't an economically viable option.