Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
That's the job of the power supplies.

So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...?

And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?

I believe most people who read this thread will understand the context that the 100KW is the "at-the-wall" power consumption of the equipment, before any losses due to PSU inefficiencies or wiring losses downstream of the PDU.
1715651303
Hero Member
*
Offline Offline

Posts: 1715651303

View Profile Personal Message (Offline)

Ignore
1715651303
Reply with quote  #2

1715651303
Report to moderator
Whoever mines the block which ends up containing your transaction will get its fee.
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
1715651303
Hero Member
*
Offline Offline

Posts: 1715651303

View Profile Personal Message (Offline)

Ignore
1715651303
Reply with quote  #2

1715651303
Report to moderator
1715651303
Hero Member
*
Offline Offline

Posts: 1715651303

View Profile Personal Message (Offline)

Ignore
1715651303
Reply with quote  #2

1715651303
Report to moderator
sbogovac
Legendary
*
Offline Offline

Activity: 2730
Merit: 1192


I don't believe in denial.


View Profile
December 30, 2014, 06:44:20 PM
 #22

[...]
Still don't understand how this will "supply" any "watts to [12V] mining equipment [OP]" though...
That's the job of the power supplies.

So - basically - you're saying "this PDU" will not be "supplying" any "Watts to mining equipment...?

And even if you assume any role for PSU's than certainly those 100KW will not reach cet "mining equipment"...?

I believe most people who read this thread will understand the context that the 100KW is the "at-the-wall" power consumption of the equipment, before any losses due to PSU inefficiencies or wiring losses downstream of the PDU.

Possibly, but some (like the OP, maybe) won't:

I am not that good when it comes to electrical matters.  

First person to tell me (correctly) how many watts this PDU can supply to mining equipment, wins the bounty:

http://www.ebay.com/itm/PDI-PDU-100-KVA-480v-x-208v-3-Panel-Manuifactured-2009-/121527983792?pt=US_Uninterruptible_Power_Supplies&hash=item1c4ba1deb0



0x7442A5c37E513D335F53843cD20c00F77eAC7867
Trends
Member
**
Offline Offline

Activity: 119
Merit: 10


View Profile
January 01, 2015, 01:15:49 AM
 #23

Each of the 3 distribution panels (208/120 breaker panels) would have a 225 amp main breaker, not one single 225A breaker on the 208V output of the transformer.

Transformers are sized to permit 100% of their rating therefore 278 Amps (100080 watts) of 208V is avaliable for the 3 distruibution panels to share depending on connected load at each panel. In theroy it would be possible to load up the distribution panels (even following the 80% rule) to exceed the 278A output of the transformer but doing so would cause the main transformer breaker to trip on overload.
Best to have a qualified electrician or electrical eng review your plans.


Trends

Quadriga CX BTC/CAD Coin Exchange     www.quadrigacx.com/?ref=umvq5t3i2r6im243v94vucbo
ASICSPACE
Full Member
***
Offline Offline

Activity: 121
Merit: 100

Feel free to contact me via email, skype or phone!


View Profile WWW
January 01, 2015, 01:52:56 AM
 #24

Each of the 3 distribution panels (208/120 breaker panels) would have a 225 amp main breaker, not one single 225A breaker on the 208V output of the transformer.

Transformers are sized to permit 100% of their rating therefore 278 Amps (100080 watts) of 208V is avaliable for the 3 distruibution panels to share depending on connected load at each panel. In theroy it would be possible to load up the distribution panels (even following the 80% rule) to exceed the 278A output of the transformer but doing so would cause the main transformer breaker to trip on overload.
Best to have a qualified electrician or electrical eng review your plans.


Trends

Always a good idea to get a review by an expert. Some transformers can be overloaded depending on their insulation class and ambient temperature.