So a 20 amp breaker will be good enough for this miner?
no my guess is you need a 240 volt 30 amp.
not a 240 20 amp.
we have seen a demo of this gear pull 3417 watts.
depending on your voltage level say 208 to 242 you will pull 16.42 amps to 14.12 amps.
a 20 amp breaker doing 16.42 amps is not good for a 24/7/365 load. it is just over the limit.
So yeah 1 unit in a cooler space you may do it.
but 5 units or 10 units or 20 units on a warm spot and you are in trouble.
time will tell how subject they are to this issue. there are not any in the field with regular miners.
I really would have preferred them to use Bitmain's 2 plug design on the s17.
Edit HaggsFin is correct that 220 volts is good just as I am correct that 208 volts will or may be short with a 20 amp fuse.
just got tracking!!!!!!
yeah baby!!!!!