Well, there's two windows, one which wold sort of be behind the units that I can put a window fan in to exhaust and then the window AC to cool, so between that, after I put the door up I should be in a sort of sweet spot.

If you have two windows you may want to experiment with using two fans (one drawing "cool") outside air in and one forcing the hot miner air out.   Using an AC unit and an open window is probably not going to work well.
1714957004
Hero Member
*
Offline Offline

Posts: 1714957004

View Profile Personal Message (Offline)

Ignore
1714957004
Reply with quote  #2

1714957004
Report to moderator
1714957004
Hero Member
*
Offline Offline

Posts: 1714957004

View Profile Personal Message (Offline)

Ignore
1714957004
Reply with quote  #2

1714957004
Report to moderator
1714957004
Hero Member
*
Offline Offline

Posts: 1714957004

View Profile Personal Message (Offline)

Ignore
1714957004
Reply with quote  #2

1714957004
Report to moderator
Bitcoin mining is now a specialized and very risky industry, just like gold mining. Amateur miners are unlikely to make much money, and may even lose money. Bitcoin is much more than just mining, though!
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
MoreBloodWine (OP)
Legendary
*
Offline Offline

Activity: 1050
Merit: 1001


View Profile
May 03, 2014, 10:35:40 PM
 #22

Well, there's two windows, one which wold sort of be behind the units that I can put a window fan in to exhaust and then the window AC to cool, so between that, after I put the door up I should be in a sort of sweet spot.

If you have two windows you may want to experiment with using two fans (one drawing "cool") outside air in and one forcing the hot miner air out.   Using an AC unit and an open window is probably not going to work well.
I'll try that but why would you say the window AC wouldnt work too well ?

It's got the side blades that pull out to close off the openings on the side.

I mean ya, it wouldnt be air tight bu it should cool a good bit with one window having an exhaust fan blowing out to draw hot air.

Edit: Window fans are same way, side blades that pull out to block openings to the side.

To be decided...
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
May 04, 2014, 12:09:59 AM
 #23

Nothing wrong with a window AC unit.   A window AC unit plus an open window venting to the outside is probably not going to work as well as you think.  If air is flowing out the window that air has to come from somewhere and it is most likely going to come from the rest of your house so it would be like running your house AC with a window wide open.

AC + sealed environment = good
no AC using forced air cooling to cool with outside air = good
AC + outside air = not good

Although experiment and see.
ssateneth
Legendary
*
Offline Offline

Activity: 1344
Merit: 1004



View Profile
May 04, 2014, 12:21:54 AM
 #24

I jimmied together something that converts a dryer socket into 8 plugs. Powered almost 7 kilowatts worth of equipment without issue. I should probably sell it... Also have power cables with appropriate plugs that plug right into ATX power supply.




DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
May 04, 2014, 12:30:27 AM
 #25

If you sell it, it would be wise to limit it (via internal breaker) to 24A.  Continual loads must be derated by 20% per the NEC.   In reality this is probably excessively conservative however if something goes wrong an insurance company is going to look for some way to shift liability. 
MoreBloodWine (OP)
Legendary
*
Offline Offline

Activity: 1050
Merit: 1001


View Profile
May 06, 2014, 03:53:19 AM
 #26

Still trying to figure out if two window fans will be enough provided the 5,220w figure doesn't go any higher than that.

You ever experiment with a window fan setup using two windows, one to draw and the other to exhaust ?

The heat should with luck be drawn out quickly and not be able to build up with where the units will be sort of diagonal to the ehaust window.

But then there's the issue of the outside air temp being drawn in ;-/

To be decided...
MoreBloodWine (OP)
Legendary
*
Offline Offline

Activity: 1050
Merit: 1001


View Profile
May 08, 2014, 12:46:24 AM
Last edit: May 08, 2014, 02:28:03 AM by MoreBloodWine
 #27

Yeah assumming your numbers are correct you have 3 units @ 1440W ea and 9 units @ 100W ea for total of 5220W.  Keep in mind is mind that 5220W is 18,000+ BTU/HR of heat which will need to be removed.  If it isn't removed the temp will continually increase.

So if the door is shut then you are going to need to cool most of that with the window unit (the house AC unit isn't going to run continually).  I don't know if they make 18,000 BTU/HR Window AC Units which run on 120V and use less than 15A.  If they don't you may need to scale back.  Without an AC unit you would need one massive (and loud) fan) to exhaust that heat from the room and bring in "cool" summer outdoor air.

Looks like fans by themselves, even with one going out and the other in and almost opposites of the are wont work.

So looks like I will have to try the AC thing, don't have anything in the way of 18k BTU window AC. But I do have a floor model AC on wheels I almost forgot about. I checked it earlier and the sticker rated it 12k.

Sad part is out house doesn't have regular AC. So... if I can close off the laundry area with a door to seal it off from he kitchen, I'm hoping the 12k AC I have will do the trick by itself.

I could try to use a window AC as well, it's rated 5,300 but I don't ant o chance tripping the regular breakers they'd both be on. Maybe I an use my killawat on the floor model tomorrow to check it out.

But what do you think of the 12k floor model by itself ?

Edit: So this eBay sellers on a bunch of f'in crack !

http://cgi.ebay.com/ws/eBayISAPI.dll?ViewItem&item=111348176399

Had listed at $60, no one bought it, told him I would buy it for $45 since it's a heavily used / aged PDU. HE responds by saying it's already below market value. So what's he do when the listing ends with no interest and one watcher which was me ?

He relists it with a $15 increase at a new BIN of $75... how stupid can some people be.

So ya, while I need a 12port PDU, I'm also not gonna bee a dumb ass and get ripped off.

Any other thoughts on a good 12 port PDU DeathAndTaxes ?

Say something I could get $50 or less shipped ?

Preferably something that doesn't have restrictions like 12a per row of plugs since with the way some of the equipment breaks down will mean I can't use all of it if there's amp restrictions per row of plugs.

ex: Two rows of 6 plugs for total of 12.

To be decided...
DeathAndTaxes
Donator
Legendary
*
Offline Offline

Activity: 1218
Merit: 1079


Gerald Davis


View Profile
May 08, 2014, 10:04:34 PM
 #28

Well there are some assumptions so estimates and theories only take you so far you probably are going to have to experiment.

However lets assume that the heat output of your rigs IS exactly 18K BTU/HR and the AC unit can remove exactly 15K BTU/HR.  The temp in the room will rise.  You are adding 3K BTU into the room every hour.  It would be no different than right now putting a 3K BTU/HR space heater in there (no AC).  If the room was perfectly insulated the temp would keep rising forever until either the heater melted or the power cord caught on fire.

In the real world no room is perfectly insulated so there is going to be some heat loss through the walls however the rate of heat transfer depends on the difference in temperatures.  So to move 3K excess thermal energy out of the room when the outside air is say 80F probably means the room temp would rise until it reached equilibrium at 140F maybe 160F.

Now it is possible that your AC unit has more than 12K BTU cooling capacity.  Normally the capacity is rated at a certain temp differential (i.e. 90F outside 70F inside).  The cooler it is outside, and the warmer it is inside the more efficient the unit becomes.  It is also possible your estimate for the units power consumption is high and they will use less power.  You probably aren't going to know for sure until you plug them in.  However I would plan for the possibility that you either need to scale back your farm or scale up your cooling.  Then there are other factors which will vary a lot.  If you live in AZ and the room the miners are in is south facing then room is going to acquire more heat from the sun than say a shaded room on the north side of the house in Maine.

So like I said you can estimate, and plan but eventually you are going to need to plug everything in and take some measurements.  If you live in a part of the country which has dry heat you may want to look at an evaporative cooler (swamp cooler).  If you live somewhere which is humid that is pointless though (they cool by adding moisture to their air, the more moisture that is already in the air naturally the less cooling capacity they have).

Quote
Any other thoughts on a good 12 port PDU DeathAndTaxes ?

Not really although any unit with a NEMA L6-30 plug is going to basically be the same so you don't need to stick to APC.  I mean these are essentially just industrial grade power strips.  Since they are being sold as used surplus I have seen them as cheap as $30 and as much as $90.  It is just the luck of the draw I guess.