[quote authocircuits.ey link=topic=671761.msg7695725#msg7695725 date=1404608378]
I have 5 S1's
5 S1s will pull almost 2000 watts. A residential 115V 15A circuit will only handle about 1400 watts. Even a 20A circuit will only run 1900 watts.
If you want to run all 5 on the same circuit, you should consider having a 220V 20A circuit installed which will make the PSUs run more efficiently or you can spread the units across multiple circuits in your house
I would definetly do as Bbeesley suggests. I ran 2 20A Dedicated outlets into my office for the mining pool I have as I had the same problem with 2 miners & 3 PCs in my office.
It took the electrician ~2h to run the line from the 1st Story Panel box to 2nd Story and i had to buy ~$80 worth of supplies. All in it cost about $300 to get the outlets in and help prevent a fire
[/quote]
Wow american houses are wired cheap. Uk standards is 240v at 13a most houses have atleast 4 circuits downstairs sockets. Upstairs sockets. Downstairs lights. Upstairs lights.