I ran 17th and blew my 100amp main fuse (240v)

I ran 16mm2 cabling and 6mm radial sockets for all machines and cables still get warm.

Unless your sockets are wired in 10-16mm and you have 400amp three phase coming into house you won't gey over 15-20th with current miners.
mwizard
Full Member
***
Offline Offline

Activity: 203
Merit: 100


View Profile
December 17, 2014, 08:45:50 AM
 #22

Plus, 60 TH/s is only around 36 KW/h with AntMiner S4s (Supposedly), and is definitely not energy worth of 60 housholds, so that really won't be a problem at all.

I do, however, believe I will simply purchase a single AntMiner S4 at first to prospect, because if it doesn't give me what I want, I can always re-sell it.

Anyone half one that can rep it to give me an idea of what to expect?

36 KW for 60 TH/s implies 0.6 watts/gigahash which I doubt an S4, and associated cooling, could do even with underclocking.

Purchasing and testing an S4 to get an idea on what to expect sounds very sensible.

My understanding is that S4s have an "at wall" rating of 0.69 Watts/gigahash, with under clocking being able to bring this down to about 0.66 Watts/gigahash.  So 60 TH/s would require 41.4 kilowatts, plus you mentioned you are considering using air conditioning units for cooling.  This could add at least another 20%. or 4 kilowatts.  So I would aim for at least 45 KW/h to get 60 TH/s from S4s.

As an aside the original 60 households estimate is based on an average house using about 24 kWh of energy per day and 60 kW of power being used for mining.  The actual US daily electrical energy usage for a house is slightly higher than that at 30 kWh per day.   So a more accurate figure for someone mining in the US using 45 kW (1080 kWh of energy per day) for mining is equivalent to the electrical energy consumption of 1080/30 or 36 US houses.  
Jamphone
Full Member
***
Offline Offline

Activity: 125
Merit: 100


View Profile
December 17, 2014, 11:16:50 AM
 #23

I sent you a private message.
spiceminer15
Sr. Member
****
Offline Offline

Activity: 336
Merit: 250



View Profile
December 18, 2014, 12:01:01 AM
 #24

don't do it. 0.088 is way too high to make money right now. maybe if BTC was $600
bitkilo
Legendary
*
Offline Offline

Activity: 1638
Merit: 1010


https://www.bitcoin.com/


View Profile WWW
December 18, 2014, 03:05:21 AM
Last edit: December 18, 2014, 03:20:21 AM by bitkilo
 #25

I have found somehing that might suit your needs https://bitmaintech.com/productDetail.htm?pid=000201412171033028658LE40FU705ED
Perfect for you, your wife will never find out!
This is squalls thread about it
https://bitcointalk.org/index.php?topic=896602.0

notlist3d
Legendary
*
Offline Offline

Activity: 1456
Merit: 1000



View Profile
December 18, 2014, 03:13:04 AM
 #26

I ran 17th and blew my 100amp main fuse (240v)

I ran 16mm2 cabling and 6mm radial sockets for all machines and cables still get warm.

Unless your sockets are wired in 10-16mm and you have 400amp three phase coming into house you won't gey over 15-20th with current miners.

I have multiple power lines from electric company.   I have been able to do 16-17T and still have room to grow. 

It depends on price.  Go with SP20 or S4.   Your electricity is not bad.   I might suggest starting off a little smaller.  Going nothing to 20T will create a lot of possible issues.   Most homes will not be ready for 20T unless you get a electrician.  Also networking need to have it ready. 

Also something most don't mention is security.  Personally I have security with both of my mining areas.  I'm sure some skip this but I sleep safe with this.
TinCup
Newbie
*
Offline Offline

Activity: 2
Merit: 0


View Profile
December 21, 2014, 03:37:06 AM
 #27

I have found somehing that might suit your needs https://bitmaintech.com/productDetail.htm?pid=000201412171033028658LE40FU705ED
Perfect for you, your wife will never find out!
This is squalls thread about it
https://bitcointalk.org/index.php?topic=896602.0


lol.....might as well go big! 
Rewire (OP)
Newbie
*
Offline Offline

Activity: 9
Merit: 0


View Profile
December 21, 2014, 03:42:47 AM
 #28

HA!  I'm not quite sure I'm willing to spend $425k on a non-refundable investment.  I won't even spend that much on a car (at the moment) and my last vehicle cost me 112k fully loaded.  Wife wasn't happy about that one, but you know for sure I fucking am with a brand new GT-R fresh off the line.

I've ordered a single S4 and will debate getting more depending on the success and cost this one unit runs me.

Still wishing I bought a shit-ton of coins when I originally found out about BTC, it was like 20 bucks for over 10,000 at that time.  I had a friend that accidentally threw out a hard drive that had over 30,000 coins on it.  Had to stop him from killing himself, and he still bitches about it every single day I see him.  I would too probably.
aacoins
Member
**
Offline Offline

Activity: 112
Merit: 10

Run a Full Node-Just Do It!


View Profile
December 21, 2014, 07:12:06 AM
 #29

The circuitry in my house can easily handle a 100 KW/h draw from a single outlet with no issues with the current equipment, all of my wiring in the house is VERY thick.  I paid for my house to be custom built on land I purchased in 2012 with the best equipment I could afford within reasonable usage amounts, so I don't have to replace anything for a long time, and it will help retain value in-case we move.   Plus, 60 TH/s is only around 36 KW/h with AntMiner S4s (Supposedly), and is definitely not energy worth of 60 housholds, so that really won't be a problem at all.

I do, however, believe I will simply purchase a single AntMiner S4 at first to prospect, because if it doesn't give me what I want, I can always re-sell it.

Anyone half one that can rep it to give me an idea of what to expect?
Not sure what you are saying here.

100kw/h do you mean 100KWH a month or 100kw an hour because:
20 amp circuit(If you're lucky because most houses use cheaper 15 amp circuits) at 120v is only 2400 watts.

Now you can only use 80% of this safely so that leaves 1920 watts.
An Antminer s4 (Which you have stated you would like) uses 1380 watts.
So in other words per room(Because circuits are normally divided by room) you can run 1 s4 and 1 s3 Giving you 2441 Gh/s per circuit

A normal house has anywhere from 60-200 amps
You run 0 other items in your house(No lights or cooling quipment)
you get 24000 watts at best again 80 percent is 19200 watts leaving you with 11 s4 totaling 22 Th/s so your 20Th/s would be best case senario for your whole house an no other items running at all in your house.

Now you can get a service upgrade from your Power provider but this normally requires you paying a lot of money for new transformers and such. but if you would like some statistics on a s4 They fluctuate by about 5% on avg This is sometimes good sometimes bad all depends on your pool, difficulty, exterior conditions and the specific s4 you get.

Not at all trying to be mean just putting the info in the thread

BTC-1AacoiNQXHJtsVuTFZRZnX6iGXtFgHHYae
XPY-PAACoin14KZNe2sPcpFUH4SDah6LkbqPsF
Tip Jar Smiley
Rewire (OP)
Newbie
*
Offline Offline

Activity: 9
Merit: 0


View Profile
December 21, 2014, 07:44:21 AM
Last edit: December 21, 2014, 08:01:31 AM by Rewire
 #30

I meant 100 KW daily draw, put the /h by habit.  Each of the rooms in my house has 6-10 outlets of the 20 amp kind.  My wife and I usually use anywhere from 80-150 KW a day, depending on appliance usage, my computer alone with all my monitors and stuff inside it uses almost 1.7 KW/h.  I'm not certain of the specs, but I was told by the electrician that set up the house that my house could easily handle a 1,200 KW draw daily on all circuits without any worries about issues, though he wasn't sure when or what I would need that much power for.

I'm planning on buying a Tesla sometime, but I'd like to make some more money before I drop another 100k on a vehicle.  The more power available to my house increases the likelihood I can install a SuperCharger at my house.

EDIT:  I re-read your post.  The 15 amp "circuits" you're referring to are the amperage ratings of a standard 120v wall outlet, which there is most certainly not 1 per room.  Distribution is controlled by the breaker box, which is essentially a large circuit distributor, and the draw amount is requested via the outlet.  I'm halfway confident you don't know what you're talking about.  

RE-EDIT:  I understand now what you're saying, you're referring to the circuits controlling the outlets inside the breaker box.  I have 3-5 breaker circuits per room rated at 20 amps each, not including the separate circuits for all the lighting in the house that's ceiling mounted.  My house has 2 breaker boxes in the garage, both with 30 circuits each, I'm very confident in their abilities.
Rannasha
Hero Member
*****
Offline Offline

Activity: 728
Merit: 500


View Profile
December 21, 2014, 04:03:57 PM
 #31

Sweet Satoshi, can we please sort out our units of measurement.

A "Watt" (W) is a unit of continuous power. It means Joule (a unit of energy) per second (a unit of time). 1 W power draw is 1 Joule used per second. 1 KW power draw is 1000 J (or 1 KJ) per second. A KiloWatt-Hour is a unit of energy, just like the Joule, but on a different scale. 1 KWh corresponds to the amount of energy used by a 1 KW power draw for a duration of 1 hour. A device that uses 100 W, will consume 2.4 KWh in a day.

I meant 100 KW daily draw, put the /h by habit.
You mean KWh.

Quote
My wife and I usually use anywhere from 80-150 KW a day, depending on appliance usage,
You mean KWh. Also, for reference, the average US household uses about 900 KWh per month. Or 30 per day. You're 3-5 times the average US household. Are you sure you don't already have a mining operation running?

Quote
my computer alone with all my monitors and stuff inside it uses almost 1.7 KW/h.
You mean KW.

Also the number is unlikely for a single computer unless it has a high end CPU (overclocked!), (at least) 3 high end GPUs and several harddisks all being stressed to their maximum as well as several large monitors. And even then it's unlikely. A typical high end machine with a single GPU uses 300-400W when both CPU and GPU are fully loaded (which rarely happens with normal use).

Quote
I'm not certain of the specs, but I was told by the electrician that set up the house that my house could easily handle a 1,200 KW draw daily on all circuits without any worries about issues, though he wasn't sure when or what I would need that much power for.
You mean KWh.

1200 KWh per day is more than the average US household uses in a month.

Quote
EDIT:  I re-read your post.  The 15 amp "circuits" you're referring to are the amperage ratings of a standard 120v wall outlet, which there is most certainly not 1 per room.  Distribution is controlled by the breaker box, which is essentially a large circuit distributor, and the draw amount is requested via the outlet.  I'm halfway confident you don't know what you're talking about.

RE-EDIT:  I understand now what you're saying, you're referring to the circuits controlling the outlets inside the breaker box.  I have 3-5 breaker circuits per room rated at 20 amps each, not including the separate circuits for all the lighting in the house that's ceiling mounted.  My house has 2 breaker boxes in the garage, both with 30 circuits each, I'm very confident in their abilities.

Assuming the above is correct, then I do wonder what you were smoking when you came up with these requirements when your house was built. You don't design for a daily capacity that exceeds the national average monthly consumption without a good reason, I would guess.
aacoins
Member
**
Offline Offline

Activity: 112
Merit: 10

Run a Full Node-Just Do It!


View Profile
December 21, 2014, 05:47:33 PM
 #32

    I meant 100 KW daily draw, put the /h by habit.  Each of the rooms in my house has 6-10 outlets of the 20 amp kind.  My wife and I usually use anywhere from 80-150 KW a day, depending on appliance usage, my computer alone with all my monitors and stuff inside it uses almost 1.7 KW/h.  I'm not certain of the specs, but I was told by the electrician that set up the house that my house could easily handle a 1,200 KW draw daily on all circuits without any worries about issues, though he wasn't sure when or what I would need that much power for.

    I'm planning on buying a Tesla sometime, but I'd like to make some more money before I drop another 100k on a vehicle.  The more power available to my house increases the likelihood I can install a SuperCharger at my house.

    EDIT:  I re-read your post.  The 15 amp "circuits" you're referring to are the amperage ratings of a standard 120v wall outlet, which there is most certainly not 1 per room.  Distribution is controlled by the breaker box, which is essentially a large circuit distributor, and the draw amount is requested via the outlet.  I'm halfway confident you don't know what you're talking about.  

    RE-EDIT:  I understand now what you're saying, you're referring to the circuits controlling the outlets inside the breaker box.  I have 3-5 breaker circuits per room rated at 20 amps each, not including the separate circuits for all the lighting in the house that's ceiling mounted.  My house has 2 breaker boxes in the garage, both with 30 circuits each, I'm very confident in their abilities.
    WTH....Either your house is designed to grow weeb or you already have a substantial ammount of mining equipment because that means an average 1 story house has
    • 3 Bedrooms
    • 1.5 Bath
    • Living Room
    • Kitchen
    • Diningroom
    • Outdoor Power Front
    • Outdoor Power Rear
    • Washer
    • Dryer
    • Stove

    Now let's break this down you have 2 breaker boxes with 30 circuits each thats 60 circuits.
    You're telling me you have 1200 amps coming into your house right now?
    If not let's break it down by room
    3 Bedrooms * 3*20 Amp Circuits Each=180 Amps

    THAT'S MORE THAN MY WHOLE HOUSE!!!!!!!>!>!>!>!>!>!>!>!>>!<#w2MEBEWFYFGYWEAfUIVBUFVAUEGAFGUGBAI

    edit: that is only the first thing on that whole list?!?!?!?!

    Even tho you have 10 outlets in your room on 1 20 amp breaker doesnt mean they all can use 20 amps....Each breaker has 20 amps to divide between everything on that circuit including lighting and everything else. That's why I only have 1 of my s3's in my room as a heater right now because Even tho I have 4 outlets I only have 15 amps or 1800 watts My GPU's use a huge chunk of that so lets say leaves us with 1200 minus  the 360 watts for a buffer zone minus 355 for my antminer and then that leaves us with 455 Watts to distribute between my TV my speakers my DirecTv box my router my modem my lighting my phone chargers, etc. etc. [/list]

    BTC-1AacoiNQXHJtsVuTFZRZnX6iGXtFgHHYae
    XPY-PAACoin14KZNe2sPcpFUH4SDah6LkbqPsF
    Tip Jar Smiley
    spiceminer15
    Sr. Member
    ****
    Offline Offline

    Activity: 336
    Merit: 250



    View Profile
    December 21, 2014, 10:32:21 PM
     #33

    Smells like bs.

    I had 9-10th of undervolted s1 and a few s2 and a few s3 and I used 10000kwh a month

    Bill was around $700 with 5k kWh @ 0.064 and the rest at 0.068

    Mining is barely profitable at 0.064 cost.

    I have two 50amp 220v lines into my basement
    Argwai96
    Legendary
    *
    Offline Offline

    Activity: 1036
    Merit: 1000


    Thug for life!


    View Profile
    December 27, 2014, 03:15:32 AM
     #34

    Assuming the above is correct, then I do wonder what you were smoking when you came up with these requirements when your house was built. You don't design for a daily capacity that exceeds the national average monthly consumption without a good reason, I would guess.
    I am also interested to know what you were smoking, along with where you got it.

    Although $.08 per KWH is low, there is cheaper electricity available throughout the country, sometimes as low as .06 for residential customers.

    It appears that your profit estimate is gross mining revenue, and does not take into account the electric bill/costs that you will have. Once you take these costs into consideration your net profit will be much less. You also forgot to take into consideration the fact that the difficulty has risen in the past and will likely continue to rise in the future
    ProudMiner
    Full Member
    ***
    Offline Offline

    Activity: 134
    Merit: 100



    View Profile
    January 09, 2015, 04:07:52 PM
     #35

    Just buy bitcoins, with the current price below 300$, it is the most certain way to get a profit.

    nwfella
    Legendary
    *
    Offline Offline

    Activity: 1610
    Merit: 1000

    Well hello there!


    View Profile
    January 09, 2015, 07:21:35 PM
     #36

    Your electric is a little bit higher than mine here in Oregon.  Thus far I haven't ROI'd on a single piece of mining equipment so my advice would be to avoid mining altogether.  Granted, your results probably won't be quite as bad as mine as a large # of the more bogus asic manufacturers are getting shaken out everyday but I seriously doubt you'll get out of it what you put in at this point regardless of who you decide to go with.

    Buy and Hold probably your best strategy honestly but that is also hella risky right now.

    ¯¯̿̿¯̿̿'̿̿̿̿̿̿̿'̿̿'̿̿̿̿̿'̿̿̿)͇̿̿)̿̿̿̿ '̿̿̿̿̿̿\̵͇̿̿\=(•̪̀●́)=o/̵͇̿̿/'̿̿ ̿ ̿̿

    Gimme the crypto!!
    BTCish
    Full Member
    ***
    Offline Offline

    Activity: 182
    Merit: 100


    View Profile
    January 13, 2015, 10:38:15 AM
     #37

    Invest in BTC or altcurrencies, which will raise faster in value than BTC.

    Pages: « 1 [2]  All
      Print  
     
    Jump to:  

    Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!