so yea, 2 T17's per circuit then right? iirc T17's are right around 10 amp's each.
|
|
|
|
|
|
|
The forum was founded in 2009 by Satoshi and Sirius. It replaced a
SourceForge forum.
|
|
|
Advertised sites are not endorsed by the Bitcoin Forum. They may be unsafe, untrustworthy, or illegal in your jurisdiction.
|
|
|
|
Epochjump
Member
Offline
Activity: 129
Merit: 51
|
|
September 21, 2019, 01:32:00 PM |
|
I am currently running several S17 56TH on 208V. I have randomly Amp Clamped over 20 of them at the lead wire coming from the Breaker. These units are pulling consistently 12 Amps. We all used to easily get away with using 12 gauge wire, particularly in our receptacle;e pigtails. ( so much easier to make them up ) I am rethinking this part of my grid build outs now. These new units are consistently into the double digit amperage's. I believe that 12 gauge COPPER wire can support these loads but due to the constant draw aspect of our game, it's a bit of a game of Russian Roulette as to when your wires heat up, and melt their clothing. IMHO, it's not worth the risk to save some sore fingers from twisting 10g to 10g during rig ups. 2 S17's on one 30amp Breaker gets you right at 24amps +/-. Perfectly at the 80% threshold. Run that on 10 gauge and you'll avoid that awful smell of burning electrical components. Oh....and also burning buildings. ( side note; When I amp clamp th T17 38 th they always come in under 10 amps. Again, running 3ph, 208V )
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7850
'The right to privacy matters'
|
|
September 21, 2019, 02:11:27 PM |
|
I am currently running several S17 56TH on 208V. I have randomly Amp Clamped over 20 of them at the lead wire coming from the Breaker. These units are pulling consistently 12 Amps. We all used to easily get away with using 12 gauge wire, particularly in our receptacle;e pigtails. ( so much easier to make them up ) I am rethinking this part of my grid build outs now. These new units are consistently into the double digit amperage's. I believe that 12 gauge COPPER wire can support these loads but due to the constant draw aspect of our game, it's a bit of a game of Russian Roulette as to when your wires heat up, and melt their clothing. IMHO, it's not worth the risk to save some sore fingers from twisting 10g to 10g during rig ups. 2 S17's on one 30amp Breaker gets you right at 24amps +/-. Perfectly at the 80% threshold. Run that on 10 gauge and you'll avoid that awful smell of burning electrical components. Oh....and also burning buildings. ( side note; When I amp clamp th T17 38 th they always come in under 10 amps. Again, running 3ph, 208V ) Yeah I have only the one 53t pro which pulls 2225 watts so 2225/208 = 10.7 amps but we run around 227 volts so 2225/227 = 9.8 amps. All my 30 amp circuits to l6-30r are 10 gauge under 6 foot runs. So they can do 5000 watts 5000/208 = 24.04 amps. every once in a while we shift to a low leg and volts drop as low as 187 fucks up everything. I am working with power company as to why it happens. With us gear drops out and comes back since the low volts do not last. the danger for a steady draw setup is if the low volts lasts for hours
|
|
|
|
MoparMiningLLC
aka Stryfe
Legendary
Online
Activity: 2072
Merit: 2223
EIN: 82-3893490
|
|
September 21, 2019, 02:25:03 PM |
|
My set up is more recent - mar 2018 so all the wiring even the receptacles are fully 10gauge ao i will be ok with that
|
|
|
|
PopoJeff
|
|
September 21, 2019, 08:54:02 PM |
|
I'm also kind of dancing a fine line. I had a 250' roll of 12/3 on hand already, so I wanted to use that rather than spend more money on more wire. My run is only maybe 10-12'.
12ga is safe up to 20A, but they recommend only using 80% of that capacity. So 16A. I ran two circuits, 3 outlets per circuit.
Per Bitmain site, the S17 56th (pro-53 a little less) uses 2520 watts in normal mode. 2520 watts at 240v is 10.5A. So, 5.25A per cord.
So, in my case, i can run 3 S17's, plugging into those 6 outlets, putting 15.75A thru each circuit.
I'm running out of space in my breaker box at this point, so if I decide to add more miners, I either have to wire up a sub-panel for miners, or consolidate some of the 15A 120v circuits with tandem breakers.
BUT, now I ordered the S17e, think we're looking at 2880w (12A)....... I might be swapping out to 10ga wire.
Currently running (1) S17 56th, (1) S17 Pro 50th, and (1) S9i.... when the S17e arrives in November, the S9 will be sold on eBay. Depending how the near future plays out, I'm considering expanding a bit and running up to (5) S17's
|
Home garage miner: (3) S19j pro
|
|
|
MoparMiningLLC
aka Stryfe
Legendary
Online
Activity: 2072
Merit: 2223
EIN: 82-3893490
|
|
September 21, 2019, 10:21:48 PM |
|
I have 400 amp service coming in - 200 to the house and 200 to the miners sub panel
|
|
|
|
Epochjump
Member
Offline
Activity: 129
Merit: 51
|
|
September 22, 2019, 02:37:55 AM Last edit: September 23, 2019, 09:41:45 AM by frodocooper |
|
Yeah I have only the one 53t pro which pulls 2225 watts so 2225/208 = 10.7 amps
but we run around 227 volts so 2225/227 = 9.8 amps.
All my 30 amp circuits to l6-30r are 10 gauge under 6 foot runs. So they can do 5000 watts 5000/208 = 24.04 amps.
every once in a while we shift to a low leg and volts drop as low as 187 fucks up everything.
I am working with power company as to why it happens.
With us gear drops out and comes back since the low volts do not last.
the danger for a steady draw setup is if the low volts lasts for hours
Are these drops possibly due to Power Company changeover from one transformer to another? In one of my locations, I'm pulling 3MW off a residential substation, but I'm the only "commercial entity" drawing from that portion of the grid, I've been lucky to have very steady supply flow on the power company side. I know some residential grids can have decent size variances on their supply side. In my other location I'm pulling 4 MW's off the HV lines at through a 3500 KVA Transformer to 480V and stepping it down into containers to 3 phase 208. So far I've had very good results in my container build outs. 480V down to 208V into 10 gauge runs on 400 amp panels loaded with 30 amp breakers. Very stable so far.
|
|
|
|
Sundance_
Newbie
Offline
Activity: 20
Merit: 10
|
|
September 23, 2019, 10:45:50 AM |
|
I'm suggesting that the T model is basically just as reliable but it is in some way a model made from the less desirable cuts from wafers. Could there be in any thing resembling the truth in this or am I completely off the mark? I've not paid attention to mining for two months and I've forgotten a lot it seems.
Long story short: What is the fundamental difference between the T and S series?
Hi guys, thanks for the replies. I was wondering if anyone had any remarks on the much more wildly speculative part of my post. Whether it works out that the T model is just a model made in lesser quantities from the mishandled/malformed parts? Surely there are waste/scrap parts from making an S model that are still somewhat valuable? Bitmain is too 'insert adjective depending on your opinion of bitmain' to throw away?
|
|
|
|
Epochjump
Member
Offline
Activity: 129
Merit: 51
|
|
September 23, 2019, 08:59:17 PM Merited by frodocooper (3) |
|
I don't know enough about Chip Technology to comment intelligently on this but I do own a lot of "T" models and have first hand experience with them. I see that BM is constantly tweaking and fiddling with the 7nm density chip sets, and finding higher and better efficiency levels. While small variances to be sure, there are still notable differences. I find the "T" versus the "S" designation to be analogous to the high end car manufacturers, giving different badges to their performance and luxury lines. Porsche for Example an "S" model of any platform usually indicates a higher performance characteristic. From my experience, the "T" models are showing better reliability because they aren't running at the proverbial "redline". I feel that the S17 56 and or 64 TH units are running at the red line. Horsepower sacrifices reliability in most engineering applications. Again, just a guess based on my experience, but I will say this. My T15's, T17's are the most reliable ASIC miners I've dealt with since the S-9's. I've had ZERO issues with them. I have constant RMA's and failed boards from the less robust S grouping. Again, just one person's experience. Others may see the opposite.
|
|
|
|
mochaaa
Jr. Member
Offline
Activity: 76
Merit: 3
|
|
September 24, 2019, 06:57:30 AM |
|
pretty sure the "T" is lower quality silicon vs the "S". Either that or its 7nm vs 7nm+ of newer processes.
|
|
|
|
Thetaj
|
|
September 25, 2019, 06:17:53 AM |
|
I can say from experience that running 2 S17s on a 32amp circuit is a pretty bad ordeal.
If you really wanna go at it long term, 1 dedicated 16amp breaker for each machine is a far better choice. However, it might need to be retooled from whatever you are running before.
I used to run 4000W per each phase over a 24amp circuit. A headache to switch them all for sure.
|
|
|
|
Solicitor
Newbie
Offline
Activity: 5
Merit: 2
|
|
October 30, 2019, 01:54:08 PM |
|
Did anyone notice that Jihan Wu said on WDMC that in S17e they used revised 16nm asics? That can't be true I guess. Maybe he meant to refer to S9se which would have made more sense. Any ideas?
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7850
'The right to privacy matters'
|
|
October 30, 2019, 02:05:00 PM |
|
Did anyone notice that Jihan Wu said on WDMC that in S17e they used revised 16nm asics? That can't be true I guess. Maybe he meant to refer to S9se which would have made more sense. Any ideas?
Most likely a misspoken sentence. The S17e has a 45 watts a th rating.
|
|
|
|
Solicitor
Newbie
Offline
Activity: 5
Merit: 2
|
|
October 30, 2019, 02:15:12 PM |
|
I guess so, but made me nervous at first because he said we will do the same with S17 and ifthat would happen all those innosilicons and avalons would become pumpkins (not that they're doing very well now though)
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7850
'The right to privacy matters'
|
|
October 31, 2019, 01:44:12 AM |
|
I guess so, but made me nervous at first because he said we will do the same with S17 and ifthat would happen all those innosilicons and avalons would become pumpkins (not that they're doing very well now though)
s17 pro can do 36 watts a th and 43th nothing touches this.
|
|
|
|
Epochjump
Member
Offline
Activity: 129
Merit: 51
|
|
October 31, 2019, 03:23:56 AM Last edit: October 31, 2019, 11:40:50 AM by frodocooper |
|
s17 pro can do 36 watts a th and 43th nothing touches this.
If I could I would only run these units.
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7850
'The right to privacy matters'
|
|
October 31, 2019, 10:23:57 PM Last edit: November 01, 2019, 01:05:04 AM by frodocooper |
|
If I could I would only run these units.
Yeah in a world of phil gets his way I would have 200 of them. Hell 2000 of them.
|
|
|
|
prpz
Member
Offline
Activity: 81
Merit: 43
|
|
November 05, 2019, 04:32:15 PM |
|
Has one received any tracking info? have they started sending shipments out yet? I know orders went live at 7am eastern time I placed mine at 7:06 I know its Nov1-Nov10 was hoping that 6 min didn't set me back 8-10 days lol based on their first placed order first shipped system. or is it a general delay with these S17Es
|
|
|
|
philipma1957
Legendary
Offline
Activity: 4116
Merit: 7850
'The right to privacy matters'
|
|
November 05, 2019, 05:09:32 PM |
|
Has one received any tracking info? have they started sending shipments out yet? I know orders went live at 7am eastern time I placed mine at 7:06 I know its Nov1-Nov10 was hoping that 6 min didn't set me back 8-10 days lol based on their first placed order first shipped system. or is it a general delay with these S17Es
No they have yet to ship my t17e's ordered in sept for 1-10 nov . most likely these will start shipping on thursday or friday 7 or 8. I am not a bitmain fan. But they have been very good at being on time this year. They have not been very good with coupon distribution they still owe me 2x 57 coupons and they owe my partner 2x 57 coupons. Which is a shame as we would buy more gear with those coupons. They have also lacked clarity with location of shipments. IE if the gear is assembled in and ships from Malaysia it saves USA buyers 25% in tax. So they are batting 1 for 3 ie> on time they are good.
|
|
|
|
|