Pages: « 1 ... 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 [259] 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 ... 416 »
  Print  
Author Topic: ANTMINER S7 is available at bitmaintech.com with 4.86TH/s, 0.25J/GH  (Read 527640 times)
citronick
Legendary
*
Offline Offline

Activity: 1834
Merit: 1080


---- winter*juvia -----


View Profile
December 13, 2015, 06:19:48 AM
 #5161

Dmwardjr,
I am looking at your setup and just completed my 100amps setup at my outdoor shed.
My electrical knowledge is limited and need some advise.
I measured that each S7 draws about 5-6amps @ 1200watts each.
I use Bitmain 1600 PSUs for all the S7s I have currently.
I have 4 x S7s and intend to setup 6 more S7s.
10 x S7s is my maximum that I can afford for electricity.
How many S7s can I hookup with 80% load?
How many S7s will you hookup to your 600amp monster?

Thanks
TMT

I just got back from a birthday party.  I'll answer you properly in a PM.  Give me a little time.  I also need to know which batch S7's you have at present.  Depending on the batch, some may consume more watts (power) than others.
......

Thanks Dave for the detailed explanation.

My electrician setup 5 x 240v/20amp, 2-pole; with advise that only 2 or max 3 x S7 per point.
After reading your post, 10 x S7s should be good to go, even with the 75%/80% load safe zone.
Thanks again for the guide and keep us posted on the 600amp setup.


If I provided you good and useful info or just a smile to your day, consider sending me merit points to further validate this Bitcointalk account ~ useful for future account recovery...
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 06:21:43 AM
 #5162


Thanks Dave for the detailed explanation.

My electrician setup 5 x 240v/20amp, 2-pole; with advise that only 2 or max 3 x S7 per point.
After reading your post, 10 x S7s should be good to go, even with the 75%/80% load safe zone.
Thanks again for the guide and keep us posted on the 600amp setup.

Sure...

However, I'm still reading NEC 220.  It's long as hell.

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
citronick
Legendary
*
Offline Offline

Activity: 1834
Merit: 1080


---- winter*juvia -----


View Profile
December 13, 2015, 06:29:31 AM
 #5163

You're talking about an MSP. An MSP = main service panel. PANEL. MSB = main service breaker. All breakers are to be derated to 80% if used 100% for more than 3 hours, unless specifically rated for 100% use 24/7. Why do you need to know what page it is? Why are you so reluctant to admit that everyone is right and you're wrong about the MSB? (seems this isn't the first time you've argued about this judging from your earlier comment)

Instead of asking me for more proof and telling me you don't want opinions, prove to me that a MSB doesn't have to be derated. Your opinion doesn't count. I want cold hard facts as proof. Until then, please don't endanger people with advice that you're not 100% sure about, and please consider your own safety in regards to running your own MSB at 100%.

It's taking me a while.  I'm still reading Article 220

On the MSB, MSP thread with Prelude, I am also consulting my electrician if everything is in order, just to be 100% ok.

If I provided you good and useful info or just a smile to your day, consider sending me merit points to further validate this Bitcointalk account ~ useful for future account recovery...
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 06:31:23 AM
 #5164

You're talking about an MSP. An MSP = main service panel. PANEL. MSB = main service breaker. All breakers are to be derated to 80% if used 100% for more than 3 hours, unless specifically rated for 100% use 24/7. Why do you need to know what page it is? Why are you so reluctant to admit that everyone is right and you're wrong about the MSB? (seems this isn't the first time you've argued about this judging from your earlier comment)

Instead of asking me for more proof and telling me you don't want opinions, prove to me that a MSB doesn't have to be derated. Your opinion doesn't count. I want cold hard facts as proof. Until then, please don't endanger people with advice that you're not 100% sure about, and please consider your own safety in regards to running your own MSB at 100%.

It's taking me a while.  I'm still reading Article 220

On the MSB, MSP thread with Prelude, I am also consulting my electrician if everything is in order, just to be 100% ok.

Sounds good.  Better safe than sorry.  I couldn't find but portions of Article 220 online.  So, I just bought NEC 2014 for kindle.  I'm about to read it from there now.

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
Prelude
Legendary
*
Offline Offline

Activity: 1596
Merit: 1000



View Profile
December 13, 2015, 06:32:25 AM
 #5165

The 270A rating is for inrush, or peak current before tripping I believe. Has nothing to do with the breakers 200A rating, or it's 80% derating.

You'll be reading for a while, Dave. Tongue You won't find anything contradicting what I've said about derating the MSB.

Are you currently running your MSB maxed out at 200A?
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 06:35:20 AM
 #5166

The 270A rating is for inrush, or peak current before tripping I believe. Has nothing to do with the breakers 200A rating, or it's 80% derating.

You'll be reading for a while, Dave. Tongue You won't find anything contradicting what I've said about derating the MSB.

Are you currently running your MSB maxed out at 200A?

Prelude,

Ease up, please...

You cannot see my face or hear my tone, because I have no "tone."  Don't think this is a fighting match or an argument cause it's not.  I told you if you are correct, I will agree.  Yet, you continue to have "tone."  Or at least it appears that way.

I'm not looking for anything to "contradict," Sir.  I'm looking to see if it says what you posted.  If it does, then I will agree.  It's that simple.  I might learn something here.  Ease up.

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
Prelude
Legendary
*
Offline Offline

Activity: 1596
Merit: 1000



View Profile
December 13, 2015, 06:35:34 AM
 #5167

You're talking about an MSP. An MSP = main service panel. PANEL. MSB = main service breaker. All breakers are to be derated to 80% if used 100% for more than 3 hours, unless specifically rated for 100% use 24/7. Why do you need to know what page it is? Why are you so reluctant to admit that everyone is right and you're wrong about the MSB? (seems this isn't the first time you've argued about this judging from your earlier comment)

Instead of asking me for more proof and telling me you don't want opinions, prove to me that a MSB doesn't have to be derated. Your opinion doesn't count. I want cold hard facts as proof. Until then, please don't endanger people with advice that you're not 100% sure about, and please consider your own safety in regards to running your own MSB at 100%.

It's taking me a while.  I'm still reading Article 220

On the MSB, MSP thread with Prelude, I am also consulting my electrician if everything is in order, just to be 100% ok.

That's the best thing you can do. If there were a fire in your house, even non electrical, your insurance would deny your coverage if they see an improper electrical setup.
Prelude
Legendary
*
Offline Offline

Activity: 1596
Merit: 1000



View Profile
December 13, 2015, 06:42:20 AM
 #5168

The 270A rating is for inrush, or peak current before tripping I believe. Has nothing to do with the breakers 200A rating, or it's 80% derating.

You'll be reading for a while, Dave. Tongue You won't find anything contradicting what I've said about derating the MSB.

Are you currently running your MSB maxed out at 200A?

Prelude,

Ease up, please...

You cannot see my face or hear my tone, because I have no "tone."  Don't think this is a fighting match or an argument cause it's not.  I told you if you are correct, I will agree.  Yet, you continue to have "tone."  Or at least it appears that way.

I'm not looking for anything to "contradict," Sir.  I'm looking to see if it says what you posted.  If it does, then I will agree.  It's that simple.  I might learn something here.  Ease up.

I meant no offense at all. I was poking fun with the Tongue. Sorry if I came across badly. I'd be happy to be proven wrong since I'd be able to add another 40A of gear in my garage. Unfortunately, I know I won't be because I've done extensive research and my master electrician father-in-law has confirmed the 80% rule to me in the past.
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 06:56:18 AM
 #5169

I meant no offense at all. I was poking fun with the Tongue. Sorry if I came across badly. I'd be happy to be proven wrong since I'd be able to add another 40A of gear in my garage. Unfortunately, I know I won't be because I've done extensive research and my master electrician father-in-law has confirmed the 80% rule to me in the past.

Thumbs Up...

I wish now I had not ordered kindle version.  It's taking longer.  Harder to navigate than a book in your hand.  I'm still reading.  If you are correct, [which you may very well be] this means I will spend the extra bucks on a MSB UL listed for 100% use.  That would be cheaper than having them install 750 amps to only use 80% of it.  No?

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
Prelude
Legendary
*
Offline Offline

Activity: 1596
Merit: 1000



View Profile
December 13, 2015, 07:16:19 AM
 #5170

You might be surprised, breakers get real expensive real fast. I was holding an 4000$ 800A industrial breaker a few days ago. Don't forget that the 100% rated breaker isn't the only requirement, you need a (much?) bigger panel than normally to allow better air cooling, and I believe 90c rated wire but using 75c rated ampacity on it for heatsinking purposes.
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 07:22:11 AM
 #5171

You might be surprised, breakers get real expensive real fast. I was holding an 4000$ 800A industrial breaker a few days ago. Don't forget that the 100% rated breaker isn't the only requirement, you need a (much?) bigger panel than normally to allow better air cooling, and I believe 90c rated wire but using 75c rated ampacity on it for heatsinking purposes.

One would think if you have an MSB rated for 100% usage, you're okay using 15A, 20A, 30A, 40A, 50A, etc... breakers not listed at 100% by using them at 80% of their rating.  I would believe the wire connected to the smaller circuit breakers [Installed on the poles in the service panel] that are not rated at 100% would be okay to use wire rated at 60c on up to 90c.  Especially, since the load on those circuits should not exceed 80%.  No?

I would think the important thing would be to have the MSB rated at 100% continuous from all of the other breakers in the panel at 80% load?

EDIT: I'm fine with paying extra for a larger Main Service Panel.

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
dmwardjr
Legendary
*
Offline Offline

Activity: 1302
Merit: 1318


Technical Analyst/Trader


View Profile
December 13, 2015, 07:25:41 AM
 #5172

I'm seeing right now [If this exist in the NEC] it was from an older edition.  It's not in 5.2.3 of Article 220 of the 2014 NEC.  Still reading.  It could be in another location.

Follow me on Trading View for excellent signals in Bitcoin/US dollar - Bitstamp - https://www.tradingview.com/u/WyckoffMode/.  You can follow me on Twitter at https://twitter.com/ModeWyckoff My YouTube Channel: https://www.youtube.com/channel/UC8IbhpQwrTD6BozJPWnyAHA  My Discord Invite Link: https://discord.com/invite/3EJYTytaTT  My Website is in LIVE BETA: https://wyckoffmode.com/
yslyung
Legendary
*
Offline Offline

Activity: 1500
Merit: 1002


Mine Mine Mine


View Profile
December 13, 2015, 10:30:12 AM
 #5173

back to s7 topic . . .

1 of my batch 5 has been mining well since received but today 1 of it had 3 chips missing ! & also some "x" but after a reboot the "x" went away.

wrote to bmt & see how it goes. never oc'ed stock at 600 with 0ct 23 fw.

anyone have experienced this ?



power on/off, soft reboot, swap psu, cables all done but same results. psu is ok, cables ok, all no issues & lots of spare power too (2000w).

swapped psu & cables other s7 works fine so it;s not psu or cable issue.




wolfen
Hero Member
*****
Offline Offline

Activity: 770
Merit: 523


View Profile
December 13, 2015, 03:30:58 PM
 #5174

Running December 11 firmware 12 hours now on Kano, everything a ok.
Do we have an s7 power up light sequencing list?

For those about to block we salute you! AC->BTC
klondike_bar
Legendary
*
Offline Offline

Activity: 2128
Merit: 1005

ASIC Wannabe


View Profile
December 13, 2015, 03:34:11 PM
 #5175

You're talking about an MSP. An MSP = main service panel. PANEL. MSB = main service breaker. All breakers are to be derated to 80% if used 100% for more than 3 hours, unless specifically rated for 100% use 24/7. Why do you need to know what page it is? Why are you so reluctant to admit that everyone is right and you're wrong about the MSB? (seems this isn't the first time you've argued about this judging from your earlier comment)

Instead of asking me for more proof and telling me you don't want opinions, prove to me that a MSB doesn't have to be derated. Your opinion doesn't count. I want cold hard facts as proof. Until then, please don't endanger people with advice that you're not 100% sure about, and please consider your own safety in regards to running your own MSB at 100%.

I agree with Prelude on this. 80% continuous load is the universal rule of thumb. just because a breaker *can* handle continuous 100% load, or rated to handle as much as >120% surges before tripping, does not mean you should operate at max.

sure, the rules generally consider applications with longer, poorly ventilated wire runs (such as the walls of an older home), but if you care about safety you can just spend another $100-200 to put in an extra breaker and wire run. Its a lot better than risking >$50,000 in fire damage if something fails.

found this:
"If you have a branch circuit supplying nothing but �continuous loads,� then the minimum conductor size must have an ampacity of 125% of the load � 210.19(A)(1) � and the overcurrent protection must be 125% of the load � 210.20(A). Therefore, the breaker must be loaded to no more than 80% of its rating."

24" PCI-E cables with 16AWG wires and stripped ends - great for server PSU mods, best prices https://bitcointalk.org/index.php?topic=563461
No longer a wannabe - now an ASIC owner!
VirosaGITS
Legendary
*
Offline Offline

Activity: 1302
Merit: 1068



View Profile
December 13, 2015, 03:43:58 PM
 #5176

You're talking about an MSP. An MSP = main service panel. PANEL. MSB = main service breaker. All breakers are to be derated to 80% if used 100% for more than 3 hours, unless specifically rated for 100% use 24/7. Why do you need to know what page it is? Why are you so reluctant to admit that everyone is right and you're wrong about the MSB? (seems this isn't the first time you've argued about this judging from your earlier comment)

Instead of asking me for more proof and telling me you don't want opinions, prove to me that a MSB doesn't have to be derated. Your opinion doesn't count. I want cold hard facts as proof. Until then, please don't endanger people with advice that you're not 100% sure about, and please consider your own safety in regards to running your own MSB at 100%.

I agree with Prelude on this. 80% continuous load is the universal rule of thumb. just because a breaker *can* handle continuous 100% load, or rated to handle as much as >120% surges before tripping, does not mean you should operate at max.

sure, the rules generally consider applications with longer, poorly ventilated wire runs (such as the walls of an older home), but if you care about safety you can just spend another $100-200 to put in an extra breaker and wire run. Its a lot better than risking >$50,000 in fire damage if something fails.

found this:
"If you have a branch circuit supplying nothing but �continuous loads,� then the minimum conductor size must have an ampacity of 125% of the load � 210.19(A)(1) � and the overcurrent protection must be 125% of the load � 210.20(A). Therefore, the breaker must be loaded to no more than 80% of its rating."

The things are rigged/designed to trip at their designated limit.

You can design a build than can handle and goes at or higher than "100%",  then sure, but you're still going to trip the thing 4 times a day. If it doesnt trip, its because something is wrong and you might start smelling something called your whole place bursting into flames.

80% is a good safety standard for most electric stuff, both for handling spikes and for continuous loads.

Beside certain PSU, like the EVGA G2 which can handle 1200Watts but are labeled EVGA G2 1000w, 100% load is usually bad.


                      ▄▄█████▄▄
                    ▐████████████▄
                   ▄█▀▀▀▀▀▀▀██████▌
             █▄  ▄█▀           ▀▀█
              ▀▀▀███▄▄▄▄▄▄▄▄▄▄   █▄   ▄

               ▄▀▀         ▀▀▀▀▀▀▀██▀▀▀
         ▄▄▄▄▄█▄▄ ▄▀▀▄ ▄▄▄▄▄▄▄▄▄▄▄▄▄█▄▄▄▄
         ████▒▒███    ████▒▒████▌
    ▀█▄ ▀
███████▄ ███▒▒███      ██▒▒█████       ▀█▄
 ███████ ▀█▒▒████     ▄█▒▒█████▀         ▀█ ▄  ▄▄
  ██████  ▌▀▀█████▄▄▄███████▀▀            ███▄███▌
 █████████  █████▀▀█▀▀██████▌             ██████▀
 ▀█████████ ███▄  ███   ▐███▌ ▄██       ▄█████▀
     ▀▀    ▀▀███████████████▄▄████▄▄▄▄█▀▀▀▀▀
               ▀▀▀███▀▀▀      ██████▄
                               ▀▀▀▀▀

▄█████████████████████████████▄
███████████████████████████████
███████████████████████████████
███████████████████████████████
█████████▀▀█████████▀▀█████████
███████ ▄▀▀         ▀▀▄ ███████
██████                   ██████
█████▌     ▄▄     ▄▄     ▐█████
█████     ████   ████     █████
█████      ▀▀     ▀▀      █████
█████▄   ▀▄▄▄     ▄▄▄▀   ▄█████
████████▄▄▄█████████▄▄▄████████
███████████████████████████████
███████████████████████████████
███████████████████████████████
 ▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀▀
█ █
█ █
█ █
█ █
█ █
wolfen
Hero Member
*****
Offline Offline

Activity: 770
Merit: 523


View Profile
December 13, 2015, 03:48:57 PM
 #5177

At my tier 4 datacenter they give me 30 amps at 208v per circuit.
I am only allowed to use 21.6 amps, that is their safety margin.
They have halon and 24 hour eyes on.
At my house I have 30 amp circuits at 240v.
At 80% my breakers "feel" pretty hot. More than I am comfortable with really.

For those about to block we salute you! AC->BTC
PeaMine
Hero Member
*****
Offline Offline

Activity: 979
Merit: 510



View Profile
December 13, 2015, 05:36:35 PM
 #5178

I'm trying to order an S7 and the PSU but I get this error:
"Can not buy different currency once"
I have Bitcoin selected.
Anyone know a fix for this?

Datacenter Technician and Electrician.  If you have any questions feel free to ask me as I am generally bored looking at logs and happy to help during free time.
lanfeusst
Full Member
***
Offline Offline

Activity: 190
Merit: 100


View Profile
December 13, 2015, 06:11:28 PM
Last edit: December 13, 2015, 09:37:54 PM by lanfeusst
 #5179

I'm trying to order an S7 and the PSU but I get this error:
"Can not buy different currency once"
I have Bitcoin selected.
Anyone know a fix for this?
You have to order the PSU and the miner separately. This is a bug on the bitmain website that is there for some time already.




Here is some Overvolting - overclocking of my S7 Batch 1 with DPS-2000BB and J4bberwock breakout board.
Getting ~ 5660Gh/s, Voltage is 12.75 V under full load.
Power consumption at the wall is 1590Watt => 0.28J/Gh efficiency
I know it runs hot, but I need the silence.


icside
Member
**
Offline Offline

Activity: 117
Merit: 10


View Profile WWW
December 13, 2015, 06:40:53 PM
 #5180

You might be surprised, breakers get real expensive real fast. I was holding an 4000$ 800A industrial breaker a few days ago. Don't forget that the 100% rated breaker isn't the only requirement, you need a (much?) bigger panel than normally to allow better air cooling, and I believe 90c rated wire but using 75c rated ampacity on it for heatsinking purposes.

The fun ones are 1000A+, then you're required to have built-in GFI.

Another fun fact--the utility has no such requirements re: NEC and commonly runs like 1.5-2x NEC ampacity.

Pages: « 1 ... 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 [259] 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 ... 416 »