Bitcoin Forum
October 31, 2024, 11:26:07 AM *
News: Latest Bitcoin Core release: 28.0 [Torrent]
 
   Home   Help Search Login Register More  
Pages: « 1 ... 468 469 470 471 472 473 474 475 476 477 478 479 480 481 482 483 484 485 486 487 488 489 490 491 492 493 494 495 496 497 498 499 500 501 502 503 504 505 506 507 508 509 510 511 512 513 514 515 516 517 [518] 519 520 521 522 523 524 525 526 527 528 529 530 531 532 533 534 535 536 537 538 539 540 541 542 543 544 545 546 547 548 549 550 551 552 553 554 555 556 557 558 559 560 561 562 563 564 565 566 567 568 ... 725 »
  Print  
Author Topic: [ANN] Spondoolies-Tech - carrier grade, data center ready mining rigs  (Read 1260215 times)
This is a self-moderated topic. If you do not want to be moderated by the person who started this topic, create a new topic.
wh00per
Hero Member
*****
Offline Offline

Activity: 572
Merit: 500



View Profile
January 04, 2015, 03:22:07 PM
 #10341

yeah i presumed i could just run the full cgminer command line but it doesn't - it still takes it from the .conf
i may give the .conf change a bash when mmpool solves the next block
will let you know

You can always install a visual tool to copy/edit files over SSH. I'm using WinSCP, but it's not available on MAC.
http://www.megaleecher.net/Download_winscp_alternative_free_sftp_client_for_Mac_OS_X#axzz3NrmId8wD

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
edgar
Legendary
*
Offline Offline

Activity: 1848
Merit: 1001


View Profile
January 04, 2015, 03:36:52 PM
 #10342

no recommendations for .54 or .64?
stan258
Sr. Member
****
Offline Offline

Activity: 440
Merit: 250



View Profile
January 04, 2015, 04:56:38 PM
 #10343

Problems with the SP 20 not responding after changing pools. In Chrome selecting the miners IP with /reboot so far has brought them all back to life after a few mins. Avoiding a hard power cycle if you are remote in. I have not tried this after updating firmware.  I guess I will find out sooner rather then later. 
jjiimm_64
Legendary
*
Offline Offline

Activity: 1876
Merit: 1000


View Profile
January 04, 2015, 09:23:59 PM
 #10344

i just had a check on my sp30 gui and it thinks its Jan 2 2000

and none of the graphs are running.

still on firmware version: 2.5.12 though

meh, let it mine, stop babysitting  Cool


lol, y2k issue ?

1jimbitm6hAKTjKX4qurCNQubbnk2YsFw
Biffa
Legendary
*
Offline Offline

Activity: 3234
Merit: 1220



View Profile
January 04, 2015, 09:24:52 PM
 #10345

i just had a check on my sp30 gui and it thinks its Jan 2 2000

and none of the graphs are running.

still on firmware version: 2.5.12 though

meh, let it mine, stop babysitting  Cool


lol, y2k issue ?

Can mean that your network is blocking NTP connections.


- ssh to miner
- type "ntpd -d -n -q -p 1.openwrt.pool.ntp.org"
- If you see the text "Alarm clock" - your ntp is blocked. Open it.



Mine @ pools that pay Tx fees & don't mine empty blocks :: kanopool :: ckpool ::
Should bitmain create LPM for all models?
:: Dalcore's Crypto Mining H/W Hosting Directory & Reputation ::
DevonMiner
Sr. Member
****
Offline Offline

Activity: 471
Merit: 250


View Profile
January 04, 2015, 10:33:20 PM
 #10346


- ssh to miner
- type "ntpd -d -n -q -p 1.openwrt.pool.ntp.org"
- If you see the text "Alarm clock" - your ntp is blocked. Open it.


Interesting, SP10s and SP20s of mine have often reverted back to the future ... in Jan 2000 ... been a challenge to bring them back to real time.

blg42598
Hero Member
*****
Offline Offline

Activity: 867
Merit: 1000


View Profile
January 04, 2015, 10:43:10 PM
 #10347

Has anyone in the US purchased SP31 or 35 miners? It says recommended 208v outlet. How are you converting your 120v outlets that are in most homes in the US? Did you call an electrician? Thanks.
Biodom
Legendary
*
Offline Offline

Activity: 3934
Merit: 4449



View Profile
January 04, 2015, 10:49:03 PM
 #10348

Has anyone in the US purchased SP31 or 35 miners? It says recommended 208v outlet. How are you converting your 120v outlets that are in most homes in the US? Did you call an electrician? Thanks.

People either run these in hosting centers OR use dryer or electrical stove outlets (if you can convince your better half...). Sp35 would not even work on 120V.
Theoretically, IF you have two circuits nearby, you can connect each PSU (SP31 has two) to a different circuit, but
1. nothing else should be on these circuits
2. machine would be more loud and hash ~10% less.

I systematically mapped my house circuits by switching off one at the time and checking with a small lamp.
Nevertheless, i sent my SP3X for hosting, but looking forward to playing with them at home at some point when hosting prices > monthly revenue.
Fatman3001
Legendary
*
Offline Offline

Activity: 1526
Merit: 1013


Make Bitcoin glow with ENIAC


View Profile
January 04, 2015, 10:49:41 PM
 #10349

Anyone who knows what the current price drop will do to the development of new 14/16nm finfet chips?

"I predict the Internet will soon go spectacularly supernova and in 1996 catastrophically collapse." - Robert Metcalfe, 1995
samsonn25
Hero Member
*****
Offline Offline

Activity: 882
Merit: 1003



View Profile
January 04, 2015, 10:52:45 PM
Last edit: January 04, 2015, 11:03:00 PM by samsonn25
 #10350

Because SP35 at 3650 watts at 208-240 volts, would need very high amp circuit (slightly more than double) than at 110-115 volts that it cannot supply unless you double up to 208-240v


Let me see 3650 watts at 208-240 , whats that a 8800 watt load at 80% safety, then it needs a 80amp slot.  wtf.  40amp 2 pole.

Just 1 machine using almost half of average home 100 amp service.
Biffa
Legendary
*
Offline Offline

Activity: 3234
Merit: 1220



View Profile
January 04, 2015, 10:57:46 PM
 #10351

Anyone who knows what the current price drop will do to the development of new 14/16nm finfet chips?

To the development probably not much, but depending on how expensive they are to produce, the selling of the miners based on that process may be affected.

Mine @ pools that pay Tx fees & don't mine empty blocks :: kanopool :: ckpool ::
Should bitmain create LPM for all models?
:: Dalcore's Crypto Mining H/W Hosting Directory & Reputation ::
Fatman3001
Legendary
*
Offline Offline

Activity: 1526
Merit: 1013


Make Bitcoin glow with ENIAC


View Profile
January 04, 2015, 11:28:49 PM
 #10352

Anyone who knows what the current price drop will do to the development of new 14/16nm finfet chips?

To the development probably not much, but depending on how expensive they are to produce, the selling of the miners based on that process may be affected.

If they try to produce anything like that now it will end in tears. I see both Bitmain and Spondoolies chose to hold back a bit and keep developing 28nm for a bit (Bitmain already released their S5). It is looking like the clever move right now.

"I predict the Internet will soon go spectacularly supernova and in 1996 catastrophically collapse." - Robert Metcalfe, 1995
wh00per
Hero Member
*****
Offline Offline

Activity: 572
Merit: 500



View Profile
January 05, 2015, 01:49:12 AM
Last edit: January 05, 2015, 02:02:36 AM by wh00per
 #10353

Because SP35 at 3650 watts at 208-240 volts, would need very high amp circuit (slightly more than double) than at 110-115 volts that it cannot supply unless you double up to 208-240v


Let me see 3650 watts at 208-240 , whats that a 8800 watt load at 80% safety, then it needs a 80amp slot.  wtf.  40amp 2 pole.

Just 1 machine using almost half of average home 100 amp service.

Your math is wrong. With double the voltage you need half the amperage for the same power. 4000W at the wall per SP35 unit gives about 10Amps on a 208V circuit for each PSU.
A 208V 30A circuit will be enough for 1x SP35 (derated as you want it).  

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
bgibso01
Legendary
*
Offline Offline

Activity: 1218
Merit: 1001



View Profile
January 05, 2015, 02:02:01 AM
 #10354

Because SP35 at 3650 watts at 208-240 volts, would need very high amp circuit (slightly more than double) than at 110-115 volts that it cannot supply unless you double up to 208-240v


Let me see 3650 watts at 208-240 , whats that a 8800 watt load at 80% safety, then it needs a 80amp slot.  wtf.  40amp 2 pole.

Just 1 machine using almost half of average home 100 amp service.

Your math is wrong. With double the voltage you need half the amperage for the same power. 4000W at the wall per SP35 unit gives about 10Amps on a 208V circuit for each PSU.
A 208V 30A circuit will be enough for 1x SP35 (derated as you wanted it). 

I thought that when I read it also. But either way you slice it, it's a lot of energy per unit.  And a lot of cooling!
wh00per
Hero Member
*****
Offline Offline

Activity: 572
Merit: 500



View Profile
January 05, 2015, 02:13:20 AM
 #10355

yeap .. almost double of my average household consumption.

You don't need a lot of cooling for 1 unit though. It's like a 70 deg. C room heater good to keep the garage warm in the winter. In the summer, you just need to vent that heat (i.e. keep the garage door cracked, if no animals visit you .. heh).

CSA/cUL Certified Power Distribution Panels - Basic, Switched, Metered. 1-3 phases. Up to 600V. NMC:N4F9qvHz11BHcc4nh1LCJFsrZhA1EWgVwj
bgibso01
Legendary
*
Offline Offline

Activity: 1218
Merit: 1001



View Profile
January 05, 2015, 02:19:39 AM
 #10356

yeap .. almost double of my average household consumption.

You don't need a lot of cooling for 1 unit though. It's like a 70 deg. C room heater good to keep the garage warm in the winter. In the summer, you just need to vent that heat (i.e. keep the garage door cracked, if no animals visit you .. heh).

You're right, one unit is not really a problem.  I'm trying to figure out power arrangements for 8 of them and still be able to turn on the lights at the office. Smiley
notlist3d
Legendary
*
Offline Offline

Activity: 1456
Merit: 1000



View Profile
January 05, 2015, 02:27:07 AM
 #10357

yeap .. almost double of my average household consumption.

You don't need a lot of cooling for 1 unit though. It's like a 70 deg. C room heater good to keep the garage warm in the winter. In the summer, you just need to vent that heat (i.e. keep the garage door cracked, if no animals visit you .. heh).

You're right, one unit is not really a problem.  I'm trying to figure out power arrangements for 8 of them and still be able to turn on the lights at the office. Smiley

A secondary beaker will help.   Also if you are underclocking that 8 will take much less power.  Depending on your settings the amount of power needed very greatly.
bgibso01
Legendary
*
Offline Offline

Activity: 1218
Merit: 1001



View Profile
January 05, 2015, 02:32:08 AM
 #10358

yeap .. almost double of my average household consumption.

You don't need a lot of cooling for 1 unit though. It's like a 70 deg. C room heater good to keep the garage warm in the winter. In the summer, you just need to vent that heat (i.e. keep the garage door cracked, if no animals visit you .. heh).

You're right, one unit is not really a problem.  I'm trying to figure out power arrangements for 8 of them and still be able to turn on the lights at the office. Smiley

A secondary beaker will help.   Also if you are underclocking that 8 will take much less power.  Depending on your settings the amount of power needed very greatly.

Yeah, but most places here in the US don't wire one outlet per circuit.  Typically one room or more might be on the same 20a circuit.
stan258
Sr. Member
****
Offline Offline

Activity: 440
Merit: 250



View Profile
January 05, 2015, 05:40:34 AM
 #10359

yeap .. almost double of my average household consumption.

You don't need a lot of cooling for 1 unit though. It's like a 70 deg. C room heater good to keep the garage warm in the winter. In the summer, you just need to vent that heat (i.e. keep the garage door cracked, if no animals visit you .. heh).

You're right, one unit is not really a problem.  I'm trying to figure out power arrangements for 8 of them and still be able to turn on the lights at the office. Smiley

A secondary beaker will help.   Also if you are underclocking that 8 will take much less power.  Depending on your settings the amount of power needed very greatly.

Yeah, but most places here in the US don't wire one outlet per circuit.  Typically one room or more might be on the same 20a circuit.

If the building was built not cutting corners you should have some empty slots in sub panels and wiring capacity to take several breakers to 240V.  However I have run into "j conduit approved build as is" stamped on the building plans and no conduit for 20 feet. So somebody cut time or costs.

Are you based on the West Coast? Their is a strong possibility I can get you electricians to take a look at what you need.  The team does work from Washington to Texas based in Las Vegas. If they are headed to or from your area I can have them stop by.They will know what you need they did my set up few months ago. PM me if you need more info.    

 
samsonn25
Hero Member
*****
Offline Offline

Activity: 882
Merit: 1003



View Profile
January 05, 2015, 07:22:07 AM
Last edit: January 05, 2015, 07:32:09 AM by samsonn25
 #10360

Because SP35 at 3650 watts at 208-240 volts, would need very high amp circuit (slightly more than double) than at 110-115 volts that it cannot supply unless you double up to 208-240v


Let me see 3650 watts at 208-240 , whats that a 8800 watt load at 80% safety, then it needs a 80amp slot.  wtf.  40amp 2 pole.

Just 1 machine using almost half of average home 100 amp service.

Your math is wrong. With double the voltage you need half the amperage for the same power. 4000W at the wall per SP35 unit gives about 10Amps on a 208V circuit for each PSU.
A 208V 30A circuit will be enough for 1x SP35 (derated as you want it).  




Thats right.  They specified 2 x to feed the power.  Because there are not many single 4000 watt psu
Pages: « 1 ... 468 469 470 471 472 473 474 475 476 477 478 479 480 481 482 483 484 485 486 487 488 489 490 491 492 493 494 495 496 497 498 499 500 501 502 503 504 505 506 507 508 509 510 511 512 513 514 515 516 517 [518] 519 520 521 522 523 524 525 526 527 528 529 530 531 532 533 534 535 536 537 538 539 540 541 542 543 544 545 546 547 548 549 550 551 552 553 554 555 556 557 558 559 560 561 562 563 564 565 566 567 568 ... 725 »
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.19 | SMF © 2006-2009, Simple Machines Valid XHTML 1.0! Valid CSS!