You can just sit it onto the shelf and stack the units....
You do not need any special equipment for that.
A metal, heavy duty shelf is enough and off you go.
|
|
|
|
jtoomim
|
|
July 17, 2014, 02:09:39 PM |
|
I agree with Collider, stacking works fine for small numbers. Also, unless you have an unusual facility, you're not going to be able to have more than one or two SP30s in a room for power and cooling reasons.
|
Hosting bitcoin miners for $65 to $80/kW/month on clean, cheap hydro power. http://Toom.im
|
|
|
Collider
|
|
July 18, 2014, 06:01:35 AM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
|
|
|
|
zvisha
|
|
July 18, 2014, 08:06:27 AM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
About that much. Sp30 no idea yet.
|
|
|
|
Tigggger
Legendary
Offline
Activity: 1098
Merit: 1000
|
|
July 18, 2014, 08:48:59 AM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
Mine report around 1,200GH through the API and around 1,300 in the GUI/Pool so around 8% It wouldn't normally be a problem but I rent my rigs out and the site uses the API to determine the speed so they appear to purchasers as slower than they are.
|
|
|
|
Collider
|
|
July 18, 2014, 09:10:39 AM |
|
yeah, I try to control my rigs through api, as it is easier to group them.
It kind of sucks if the reported hashrate isn´t accurate.... for my internal statistics that is.
|
|
|
|
BitCoin Operated Boy
|
|
July 18, 2014, 02:10:31 PM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
I agree with Collider, stacking works fine for small numbers. Also, unless you have an unusual facility, you're not going to be able to have more than one or two SP30s in a room for power and cooling reasons.
Thanks guys. I have been thinking about leaving some space between units, so they are not directly stack up on each other, in order to have some air flow in between the units. Maybe you are right it wouldn't make a difference as I will keep them in my house in one of the rooms.
|
|
|
|
Biodom
Legendary
Offline
Activity: 3934
Merit: 4455
|
|
July 18, 2014, 10:23:22 PM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
I agree with Collider, stacking works fine for small numbers. Also, unless you have an unusual facility, you're not going to be able to have more than one or two SP30s in a room for power and cooling reasons.
Thanks guys. I have been thinking about leaving some space between units, so they are not directly stack up on each other, in order to have some air flow in between the units. Maybe you are right it wouldn't make a difference as I will keep them in my house in one of the rooms. 2 units in one of the rooms? 2 units will produce ~5.4-5.6kw equivalent of heat and will require four 15A curcuits (if you are at 110V). In my experience in regular size US bedroom, like 16' X 18', 2.2-2.3kw increased ambient temp to 33oC (from 28oC) with A/C going full blast 24hr (in summer time).
|
|
|
|
RoadStress
Legendary
Offline
Activity: 1904
Merit: 1007
|
|
July 18, 2014, 10:36:52 PM |
|
2 units in one of the rooms? 2 units will produce ~5.4-5.6kw equivalent of heat and will require four 15A curcuits (if you are at 110V). In my experience in regular size US bedroom, like 16' X 18', 2.2-2.3kw increased ambient temp to 33oC (from 28oC) with A/C going full blast 24hr (in summer time).
Why not trade the a/c for 1-3 big ass vents to move the air outside the room?
|
|
|
|
QuiveringGibbage
|
|
July 19, 2014, 10:13:53 AM |
|
Mine report around 1,200GH through the API and around 1,300 in the GUI/Pool so around 8%
It wouldn't normally be a problem but I rent my rigs out and the site uses the API to determine the speed so they appear to purchasers as slower than they are.
+1 QG
|
Bitcoin is at the tippity top of the mountain...but it's really only half way up..
|
|
|
BitCoin Operated Boy
|
|
July 19, 2014, 05:14:31 PM |
|
@zvisha
How much too low is the sp10 cgminer API readout (aka cgminer stats)?
I read through github and I suspect around 5%?
Will the sp30 have the same inaccuracy?
I agree with Collider, stacking works fine for small numbers. Also, unless you have an unusual facility, you're not going to be able to have more than one or two SP30s in a room for power and cooling reasons.
Thanks guys. I have been thinking about leaving some space between units, so they are not directly stack up on each other, in order to have some air flow in between the units. Maybe you are right it wouldn't make a difference as I will keep them in my house in one of the rooms. 2 units in one of the rooms? 2 units will produce ~5.4-5.6kw equivalent of heat and will require four 15A curcuits (if you are at 110V). In my experience in regular size US bedroom, like 16' X 18', 2.2-2.3kw increased ambient temp to 33oC (from 28oC) with A/C going full blast 24hr (in summer time). I live in UK. I can't really perform any installations at the house as it doesn't belong to me. I'm just only renting the place :-)
|
|
|
|
Soros Shorts
Donator
Legendary
Offline
Activity: 1617
Merit: 1012
|
|
July 19, 2014, 07:58:20 PM |
|
Can one SP30 be made to run off a single 120V/20A circuit?
This is a DC circuit with wiring good for 30A+ and a commercial grade PDU, so I don't intend to de-rate to 80%.
|
|
|
|
Collider
|
|
July 19, 2014, 08:44:46 PM |
|
Can one SP30 be made to run off a single 120V/20A circuit?
This is a DC circuit with wiring good for 30A+ and a commercial grade PDU, so I don't intend to de-rate to 80%.
I would not recommend it, as the internal PSUs are not going to be able to deliver the full 2.5kW to the asics. You would have your hashrate reduced by ~10%
|
|
|
|
tzortz
|
|
July 19, 2014, 09:40:20 PM |
|
So, when is the first batch SP30 going to be delivered?
|
All is Mine!
1H7LUdfx9AFTMSXPsCBror3RDk57zgnc2R
|
|
|
RoadStress
Legendary
Offline
Activity: 1904
Merit: 1007
|
|
July 19, 2014, 09:44:24 PM |
|
So, when is the first batch SP30 going to be delivered?
Well this month for sure even if there are just 10 days left.
|
|
|
|
padrino
Legendary
Offline
Activity: 1428
Merit: 1000
https://www.bitworks.io
|
|
July 19, 2014, 09:45:51 PM |
|
So, when is the first batch SP30 going to be delivered?
Well this month for sure even if there are just 10 days left. I know they are a good crew but without even having the first set of chips in you think it will really be that smooth?
|
|
|
|
tzortz
|
|
July 19, 2014, 10:38:59 PM |
|
Yes, I also worry that the time is very limited and would be some small delay of the first delivery....?
|
All is Mine!
1H7LUdfx9AFTMSXPsCBror3RDk57zgnc2R
|
|
|
Soros Shorts
Donator
Legendary
Offline
Activity: 1617
Merit: 1012
|
|
July 19, 2014, 10:51:40 PM |
|
Can one SP30 be made to run off a single 120V/20A circuit?
This is a DC circuit with wiring good for 30A+ and a commercial grade PDU, so I don't intend to de-rate to 80%.
I would not recommend it, as the internal PSUs are not going to be able to deliver the full 2.5kW to the asics. You would have your hashrate reduced by ~10% You mean it will trip the breaker? Well I am paying a flat rate for the 20 Amp circuits so I guess I would have to under-clock the SP30. Or maybe use 2 circuits and somehow find some other smaller hardware to use up the extra amps (probably S3s).
|
|
|
|
jtoomim
|
|
July 20, 2014, 04:46:12 AM |
|
Can one SP30 be made to run off a single 120V/20A circuit?
This is a DC circuit with wiring good for 30A+ and a commercial grade PDU, so I don't intend to de-rate to 80%.
No. 2750 W / 120 V = 22.92 A. The breaker will likely trip if you try to draw more than 16 amps continuous, unless it is a 100% rated circuit breaker. 100% rated circuit breakers are very rare in that size; you usually only find them in the hundreds-of-amps sizes. The 80% derating isn't something that you choose to apply. It's in the National Electric Code (although in there it's actually described as a bunch of 125% rules, where "continuous" loads are considered to be 125% of a noncontinuous load). It's what circuit breakers are designed for, and how they behave. They aren't guaranteed to trip at 80%. They're just likely to, especially if the ambient temperature goes up. (Circuit breakers use a bimetallic strip to sense the breaker's temperature and trip if it gets too hot.) At full speed and 120V, one SP30 will use about 70% of the usable capacity on two 20A circuits. You might be able to stick 300 W more on each circuit before they start tripping. Adding an Antminer would be a gamble, though it could work. Even underclocking it won't help you much. 2500 W / 120 V = 20.83 A. I'd be surprised if that didn't trip within an hour. Chances are, your situation is even worse than that. 120 V is usually used to refer to the voltage class in terms of what devices are rated to be able to accept. The actual voltage that is delivered on circuits rated for 120 V is usually around 115 V. I take it you mean this is a datacenter circuit, not a direct current circuit? 115V 20A circuits are a very expensive and inefficient way of delivering power. It will also likely cause your SP30 to underperform. You should ask your datacenter for 208 V or 230 V circuits instead. If they don't have that available, you should switch datacenters.
|
Hosting bitcoin miners for $65 to $80/kW/month on clean, cheap hydro power. http://Toom.im
|
|
|
Collider
|
|
July 20, 2014, 05:35:52 AM Last edit: July 20, 2014, 06:30:13 AM by Collider |
|
Can one SP30 be made to run off a single 120V/20A circuit?
This is a DC circuit with wiring good for 30A+ and a commercial grade PDU, so I don't intend to de-rate to 80%.
I would not recommend it, as the internal PSUs are not going to be able to deliver the full 2.5kW to the asics. You would have your hashrate reduced by ~10% You mean it will trip the breaker? Well I am paying a flat rate for the 20 Amp circuits so I guess I would have to under-clock the SP30. Or maybe use 2 circuits and somehow find some other smaller hardware to use up the extra amps (probably S3s). No, I don´t mean it would trip the breaker (which it easily could if the breaker shuts the line down at 20 amps). I mean that the PSUs in the miner will not be able to supply the full amount of power on the internal 12V circuits because it is only rated to 1050W per PSU at 120V input. Just switch to a 208V or 220V circuit, 120V circuits are a stupid idea anyway. As the month is very near its end now, I am looking forward to my sp30.
|
|
|
|
|